For a stairwell, is the egress width measured in-between toe-kicks, from inside of the handrails, or outside of the toe-kicks/walls?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
10/16/2026 07:40:18 am
The width is measured at the narrowest point, typically between the handrails. There is a 4 1/2" allowance for projections below 38" though if that's what you're referring to as a toe-kick.
Reply
Chad
10/16/2026 08:11:23 am
Matt is right. I would be more lenient and skip the toe kicks in an older, existing structure but if one or two inches is the limiting factor, you have quite the occupant load to deal in a narrow space, and I would imagine this is a very small stair. Which gives me pause.
Reply
LC
10/16/2026 08:20:33 am
Code Red has a good article on this: https://coderedconsultants.com/insights/are-you-measuring-egress-widths-correctly/
Reply
Todd Wyatt
10/16/2026 08:38:51 am
Stairway width is determined between opposing finished wall(s) and/or guard surfaces (top @ 42-IN AFF min), NOT the handrails. Handrails are permitted to project up to 4.5-IN into this required width on each side. Therefore, you do not measure from the inside of the handrails unless they project further than the allowed 4.5-IN. Trim, stringers, or toe-kicks below the handrail height (34-IN min to 38-IN max AFF) are considered acceptable baseline boundaries as long as they do not encroach past this same 4.5-IN threshold.
Reply
Ivan J. Humberson
10/16/2026 09:42:51 am
I concur with Todd Wyatt on this one - for the purposes of determining egress width capacity of a stair, the measurement is made between the walls. Projections at and below handrail height of up to 4.5 inches on each side are permitted. (This would allow for the projections of both the handrail and the toe-kick/stringers.)
Reply
10/16/2026 10:00:33 am
Todd, I stand corrected, and thanks for the encouragement to pull out my Fire Protection Handbook for the first time in a while to see the methods on which the codes are based.
Reply
Jack G
10/16/2026 11:51:19 am
Minimum stair width for occupancy of 50 is 36 inches.
Reply