How do people do elevator recall during dust-producing construction/tenant fit-outs?
I have heard smoke detectors being replaced with temporary heat detectors. I have heard bag the smoke detectors (but keep it live) and install an adjacent heat detector so that flames could melt the plastic bag. How have people done this? Before people say ask the AHJ, I am an AHJ, and I am trying to keep my constituents safe and am waffling back and forth. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Glenn Berger
12/30/2025 08:36:23 am
Typically start with NFPA 241.
Reply
Ricardo Gonzales
12/30/2025 09:29:46 am
You are correct in using heat detectors instead of smoke detectors.
Reply
Jack G
12/30/2025 11:08:40 am
Yes, heats are the key along with isolating the lobbies with clear slatted dust curtains ( like freezers) to significantly cut down on dirt, dust, and contaminating the shaft ( dirt to other floors ) .
Reply
Chad
12/30/2025 02:01:21 pm
Yes a 241 plan is critical but lets go back to 72, its not a matter of just mitigating the construction hazard, it is a losing battle trying to tent off elevator landing/lobbies.
Reply