Has anyone encountered unusually high and consistent static pressures in sprinkler systems where there is no visible fire pump?
I recently came across two examples that raised questions: - A riser in our major metro showing about 165 psi static pressure. - A five-story hotel with roughly 125 psi static pressure on every level, consistently throughout the building. In both cases, I searched extensively for a fire pump and could not find one. The buildings were on normal city water supplies, not private systems or campuses, and there was nothing obviously unusual about the sites. It made me wonder whether there are situations where some type of booster pump is being used for sprinkler systems without being readily identified as a traditional NFPA 20 fire pump? Or perhaps there is another explanation entirely. Has anyone else seen this? If so: - What was the situation? - Was there hidden pressure-boosting equipment involved? - Are there municipalities or systems where this is more common? - Or is there another explanation for maintaining these pressures throughout a building without a fire pump? Interested to hear what others have encountered. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
15 Comments
Pete H
5/19/2026 06:07:04 am
What did the flow tests at the nearest street hydrants say for the pressures?
Reply
anthony Crispo
5/19/2026 07:56:36 am
A five-story hotel with roughly 125 psi static pressure on every level, consistently throughout the building. -- For this one physics doesn't like it. You should loose ~ 20 psi from the first floor up to the 5th assuming 10 ft floors.
Reply
Stevenn Gaillard
5/19/2026 08:12:03 am
This is really dependent on the location. I have seen flow tests in some areas where the static and residual were forcing PRV's without a pump involved. And sometimes the city has pressure pumps that are higher than usual. In particular you take Park City, UT they have high pressure pumps to push water up the mountain for snow making and such. They are continually at a much higher pressure than normal. Logan UT is also another area that its not uncommon for high pressures being supplied from the city.
Reply
Josh
5/19/2026 08:18:17 am
Have you checked to see if there's a campus pump that they may be on?
Reply
Brett
5/19/2026 08:31:32 am
Did you try relieving the pressure by opening a drain valve or inspector test valve. Then check to see if the pressure returns to a high point? Perhaps a surge occurred or a pressure test was completed without relieving the excess pressure. If it returns to a high point, I would test the closest hydrant to see if it is at a similar pressure.
Reply
Dan Wilder
5/19/2026 08:44:19 am
Buildings at the low end of a water zone, especially fed from tanks or when the buildout of the upper part of that same zone occurred more recently all lead to high static situations. However, those have not gone above about 125PSI in my experience (unless a water hammer occurs).
Reply
Arthur Gould
5/19/2026 09:34:02 am
Far north Georgia 10" circulating city water main not far from Cartersville.
Reply
Dan Wilder
5/19/2026 03:08:01 pm
That is a huge amount of water coming out of a single 2½" port....how much was it shaking??
Reply
Jack G
5/19/2026 04:34:46 pm
Physics, Boyles law, you have wet systems with small air pockets thru out. Initial ground water temp about 55 degrees.
Reply
Jack G
5/19/2026 04:45:44 pm
Another consideration but not likely, reminds me of Salisbury Maryland and the Purdue corp chicken plant.
Reply
Jack G
5/19/2026 04:50:08 pm
My apology—— air pockets affect water pressure ( not temperature in my initial explanation) thank you.
Reply
Ed K
5/20/2026 08:34:37 am
"It made me wonder whether there are situations where some type of booster pump is being used . . ." I've only seen it a couple times, but some older systems have an 'excess pressure pump' to keep pressure in the system higher than supply pressure. Other parts of the country may call these something different. They are a small pump about the size of a jockey pump and typically mounted on the system riser. They were sometimes used on systems with alarm valves to prevent false alarms. Flow switches with built-in retard function can serve the same purpose.
Reply
James Art
5/20/2026 03:05:33 pm
Yes, excess pressure pumps are a great way to solve a pressure surge problem.
Reply
b
5/21/2026 08:01:10 am
Tx everyone, im cool insurance guy, so i cannot be flowing or tripping anything. There are many potential issues.
Reply
James Art
5/28/2026 03:52:58 pm
How cool? B. I was an insurance guy for many years, for both Kemper HPR, and for INA Combined Property. Yes, the insurance guy does NOT normally open the valves, etc. him or her self.