MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

High Sprinkler Demand from Many Small Rooms?

6/3/2025

15 Comments

 
We have an office building where we have performed hydraulic calculations for a light hazard occupancy, using a design density of 0.10 gpm/ft² over a remote area of 1,500 ft².

However, our calculations require 20 sprinklers to cover this area, which is huge. Typically, there are only 7 sprinklers (at -215 ft² per sprinkler) that are sufficient for 1,500 ft².

The issue comes because the office has many small rooms, each with its own sprinkler, increasing the total number within the remote area. The output is higher at 439 gpm with 20 sprinklers.

How can we correctly define the remote area to bring down the overall flow bust still comply with NFPA 13?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
15 Comments
Peter H
6/3/2025 06:09:36 am

What's the ceiling height of the office building and are you using quick response heads?

If the ceiling height is under 20'-0" and you are using quick response heads, refer to 11.2.3.2.3.1 (NFPA 13 2016 Edition) to see if you can apply a design area reduction as per code.

Reply
MOHAMMAD MASHIRUL HAQUE
6/4/2025 09:01:29 am

Dear Pete H,

The design area reduction is not permitted because the sprinkler heads used as standard response. Additionally, the AHJ is asking for the area/density method, the room design method is not permitted.

I have calculated the sprinkler demand within the remote area based on the individual coverage areas of each sprinkler (e.g., 103 sqft, 115 sqft, 92 sqft, etc.). Sprinklers located within small compartments have also been omitted. However, the AHJ has said that the calculation is incorrect.

Reply
Brett
6/3/2025 06:38:23 am

The quick response area reduction is the obvious answer as Peter H has suggested. Another potential option is to stick with a 1,500 sq. ft. area and omit sprinklers in compartments that are 55 sq. ft. or less (section 27.2.4.7.2 in the 2019 edition of NFPA 13). If you're using the 2013 edition or earlier, the 55 sq. ft. area isn't in there. It used to just say "small compartments".

Reply
Glenn Berger
6/3/2025 08:11:03 am

Actually you possibly have correctly identified the hydraulically most demanding remote area. Whether it is obstructed construction or many spaces within the remote area, you will see a higher required flow rate because of the number of potentially operating sprinklers.

You want the calculations based upon the real design not the ideal (for sprinkler flow) design.

Reply
danefre
6/3/2025 08:11:30 am

Great responses above. Try both of those before my suggestion.

Check out this Meyerfire blog post: https://www.meyerfire.com/blog/hydraulic-calculations-failing-here-are-ideas

Put in the actual spacing for the sprinklers. I have a feeling your most demanding is already at 7psi so that might be moot. In light hazard the method is area of room divided by number of sprinklers.

There are zero-hydraulic-loss flexible braided hoses available.

"Balance" the calc. Find the heads that are overflowing and connect them to a different branchline and/or try to make them more demanding.

Last resort is try a K4.2 sprinkler. Need to swap all of them as you can't use the K-factor to balance calcs. This might create future confusion but it's an option.

Reply
Dan Wilder
6/3/2025 08:11:33 am

Using small room rule and using the actual coverage of each sprinkler (vs just defaulting to a max sq footage) should be enough to allow the remote area to work.

Other option is to calc the full area, omitting sprinklers in the less than 55 sq. ft. rooms, but still applying the actual coverage areas to the sprinkler demands.

If, on the rare chance these have automatic or self-closing doors (no rating required) and the rooms are rated for at least 30 minutes, room design could be utilized.

Reply
Max B
6/3/2025 08:12:33 am

Can you use room design rule? Is every head tagged with correct pressures/flow numbers for the area its covering?
Can you use k4.2 head?

Reply
Brian
6/3/2025 08:38:36 am

Also look into 23.4.4.6.2 (2013) that lets you omit sprinklers in small rooms for calculation purposes.

Reply
Jesse
6/3/2025 09:14:31 am

As Glenn indicated, seems you found the true hydraulically remote area. A couple suggestions:

First consider ceiling height. You may be able to reduce the size of the remote area using QR sprinklers and claiming a corresponding QR reduction

Second, is Room-Design method an option?

Reply
Juan Leon
6/3/2025 09:48:18 am

Use residential 3.0 heads, use the small room rule and loop the branch lines at the end.

Reply
Anthony
6/3/2025 12:44:50 pm

How are those allowable in a full 13 building that is clearly office space?

Reply
Chad
6/3/2025 09:56:36 am

Yeah I would be surprised if you cannot use a QR reduction to drive that down a bit.

Reply
Louie Lincoln
6/3/2025 11:40:29 am

Can you reduce the area to 900 sqft.

Reply
James E Art Fire Protection Engineer (FPE)
6/4/2025 06:15:54 pm

California Adopting Ordinance allows the Quick Response reduction ONLY for Light Hazard.

Reply
Kevin
6/5/2025 09:21:06 am

Max B noted a K=4.2. These can be used with K=5.6 as NFPA 13 does not have a restriction about mixing K factors. I'm in NY and still using the 2016 NFPA 13:8.3.4.
We have run into this frequently and reducing the K factor is a simple way to reduce GPM.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT