Heat & Smoke Detectors Tie to Security Panel?

9/18/2025

8 Comments

 
A customer wants to install a burglar alarm in a new building. They would like to add fire detection to the system. The building is not required to have a fire alarm system.

Can we run the heat and smoke detection off a security panel, or do we need to have a separate FACU?

I have looked in NFPA 72 (2010 edition), and I see non-required systems in Chapter 23. I see if it is a combination system the fire signal takes priority. However, I’m still not sure if we can use a security panel.

The state is under NFPA 72, 2010 edition and 2012 IBC & IFC. Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Joe
9/18/2025 08:09:38 am

Is it UL commercial listed for combination use?

Reply
Scott
9/18/2025 02:16:58 pm

The customer was requesting to do it on the burglar panel only to save money, since it is a non-required system. I made a phone call to the AHJ and he stated since we were installing fire detection, it had to go through a listed fire panel.
The AHJ was understanding of what we were trying to do, but stated we need to be in compliance with NFPA 72 and gave some code references. We are going to do it through a fire panel.

Reply
Chad
9/18/2025 08:50:42 am

If it’s non required it still needs to be installed per 72, as you noticed in chapter 23.

Assuming it’s cross UL 864 listed, You need to follow all the directions in the installation instructions including data bus separation, which is usually overlooked.

Need to do battery calcs (probably need an aux power supply)

However if it’s just a burg panel and not cross listed to 864….. no you cannot add fire devices to it, strictly speaking.

Reply
Glenn Berger
9/18/2025 09:35:00 am

In addition to the above comments -- Are there any outputs that you are trying to achieve?

I have seen nothing but problems when trying to connect fire and security alarms together. I always recommend against going the combo path.

Reply
Robert Morgan
9/18/2025 09:47:55 am

In my jurisdiction we require any non-required systems to comply completely with NFPA 72 which includes notification devices. They also have to then comply with the Illinois ADA which requires notification in all "habitable areas", The only time they could do components of a fire alarm system without meeting all of NFPA 72 is if they were protecting for instance a valuable piece of art, or it is for a specific control function ie. elevators or fire doors/shutters.

Reply
Bruce K English
9/18/2025 01:44:01 pm

As an AHJ, I do not allow a burglar alarm panel to monitor smokes/heats unless the panel and devises are listed for combination use.

Reply
Jose R Figueroa
9/18/2025 04:59:41 pm

Yes, you can operate heat and smoke detectors using a security panel without needing a separate Fire Alarm Control Unit, provided that the panel is a combination type listed and approved for fire alarm use (e.g., per UL 864). Additionally, the entire system must comply with the requirements for combination systems as outlined in NFPA 72 (2010). If the owner is interested in this arrangement, it will require research. An approval from the Authority Having Jurisdiction (AHJ) might be necessa. I would recommend starting by looking into Johnson Controls equipment.

Reply
sean
9/18/2025 05:31:51 pm

if it is cross listed

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT