Ground Wire on Secure or Unsecure Side of SCIF?

9/2/2026

11 Comments

 
For a SCIF, where should the ground wire be bonded?

We have a project where #4 AWG ground wire is to be bonded to sprinkler (water) piping of the penetration
, but does that need to occur on the secure side or the unsecured​ side of a SCIF?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Glenn Berger
9/2/2026 08:09:01 am

Provide ground wire as required by the CTTA. In my experience, I have seen no consistency.

Reply
Robb Karlin
9/2/2026 08:18:55 am

IN SCIFS that require tempest security - you should have a red power panel designated - that power is filtered by a spec filter and that company will give you details on its install.... by law and per NFPA 70 no isolated grounds are allowed and this has always been recognized even way back to the milspec guides...so I would ground every thing including the TBC/EBC to the main ground in that power panel which is required to be in the SCIF - there is so much missing info here ... just know that separate grounds are a no no per NFPA 70 NEC art 250. send me a link or PM if you need to discuss other pitfalls - especially the fire alarm SLC/NAC/BTX cross connections/ premisis alarm connection and sprinkler cross connection at the SCIF barrier.

Reply
robb karlin
9/2/2026 08:36:47 am

further comment - the point is to shield, ground, physically isolate any potential leak point for electronic data or emf/rf signal before they leave the SCIF - so the simple answer to the question. is the quickest path to ground on SCIF side - as well, its physically can not be removed unless your in the secure area - For example - the easiest means to eavesdrop on a SCIF is to tap into an improperly installed FA/MNS speaker circuit.

Reply
robbk
9/2/2026 09:04:55 am

BTW Someone needs to orchestrate the grounding bonding plan... typically metallic pipes penetrations such as cross mains are incorporated with the shielding, raised floor, equipment racks, and signal reference grid bonding connections... the bond wire would be attached to the nearest SBB (TGB)

Reply
Jon N
9/2/2026 10:52:29 am

How about giving explanations for all of the acronyms? 30+ years reviewing fire sprinkler and alarm systems and I have no idea what the following mean: (SCIF, SBB, TGB, CTTA, BTX, MNS). Please, let's talk in English so everyone benefits from the information.

Reply
Dave
9/2/2026 12:31:37 pm

Along those lines (but perhaps another topic), us sprinkler guys should understand the difference between bonding and grounding, for when we see it on site.

Reply
Brett
9/2/2026 01:47:43 pm

I'll fill in the gaps on the two that I know, but I agree it would be great for an expert to define these acronyms.

SCIF = Secure Compartmented Information Facility. Basically a room with very sensitive information that needs to prevent people from eavesdropping. I've run into these with Department of Defense projects and they never actually tell you what they do in the SCIFs in my experience. Some smarter people than me can tell you how the eavesdropping is prevented. In my experience it's been metal shielding but there are a lot of electrical engineering requirements that go into it.

MNS = Mass Notification System which is defined in NFPA 72.

Reply
BK
9/2/2026 12:58:11 pm

2022, 13:16.16 does touch on Bonding and Grounding to sprinkler pipe. I will leave this here if helpful. As with Jon, I am not versed with (SCIF, SBB, TGB, CTTA, BTX, MNS) so maybe it does not apply. However, based on 16.16, I would have to say don't use sprinkler pipe unless per 16.16.2.

Reply
Glenn Berger
9/2/2026 03:45:40 pm

CTTA - Certified TEMPEST Technical Authority - This person is the AHJ for these rooms.

Reply
Jack G
9/2/2026 05:53:46 pm

You must consult CTTA ( certified tempest technical authority ) for grounding a SCIF( Sensitive compartment information facility) the main safety and shielding wires must be bonded on an Internal Isolation Ground Bus Bar( IGBB) located inside the SCIF, which is then tied directly to the facilities main external building ground.
Inside the SCIF: Install a dedicated IGBB inside the secure room perimeter. All RF ( Radio frequency) shielding materials metal conduits filters and equipment grounds inside the SCIF must be tied to this single internal point to prevent electromagnetic interference and signal leakage ( TEMPEST).
WHILE internal elements terminate inside, the primary ground must penetrative the exterior, and bond securely to the facilities overall grounding electrode on the outside.
So both inside and outside.
Exact details / specifications should be in the facilities CSP* Construction Security Plan)

Reply
Jack G
9/2/2026 06:40:03 pm

Yes—— the size of the external ground wire must be
#4AWG. Sorry I didn’t include that above but that information was correct.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT