We are having a debate between our office and the field.
What numbers are we looking for at the initial forward flow test? The office claims we are looking for the full flow possible from the riser testing arrangement, with a minimum flow rate equal to system demand. Pressure is to be noted but not have a requirement. (The pressure is to be noted for future tests to assess system degradation.) The field claims we are looking for Flow and Pressure of the demand of the sprinkler system. Achieve flow and throttle the discharge to achieve the sprinkler system minimum required pressure for system acceptance. NFPA 13, 2019 Edition, Section 16.14.5.1 and A.16.14.5.1 address this "tests at a minimum flow rate of system demand including hose allowance where applicable" and the appendix "this test is only concerned with testing at the proper flow rate." What are your thoughts? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments
Mike Morey
8/31/2026 08:14:44 am
It's like the inverse of a main drain test, you're only concerned with the flow. The arrangement of the forward flow testing apparatus is not analogous to what was calculated. The pressure readings during a forward flow test are only useful for future comparisons, not comparisons to hydraulic calculations.
Reply
M. Newell
8/31/2026 08:16:42 am
You are only looking to make sure the backflow can supply the demand flow rate.
Reply
Dan Wilder
8/31/2026 08:21:47 am
For the initial test, NFPA 13 has this info.
Reply
Dan Wilder
8/31/2026 08:28:26 am
and that was for Main drain, not backflow.....ugh...
Reply
Bruce Edward Seiler
8/31/2026 08:34:05 am
I believe you are referencing the 2019 Edition of NFPA 13. The sections you reference above are for the Main Drain Test which does only require pressure and not gpm.
Reply
Dan Wilder
8/31/2026 08:39:57 am
Don't tell me how to read a question incorrectly only to realize after I hit Submit and see the actual question.....
Shawn S
8/31/2026 08:22:03 am
The full forward flow test is only concerned with a volume (GPM) of at least the system demand can be achieved. The standard is fairly clear on that issue. I have seen AHJ's use the full forward flow test as a validation of the BFP friction loss, or the validation of the water supply. It is simply an exercising of the BFP. Being on the AHJ side, there remains a fair amount of misunderstanding of this issue on both sides of the table.
Reply
Glenn Berger
8/31/2026 08:37:34 am
It sounds like both sides are correct. Initially the look is for pressure and flow at the riser, which can/will be used as future reference for supply side changes in flow.
Reply
Bruce Edward Seiler
8/31/2026 08:38:21 am
I would agree with the comments above stating GPM is the only requirement for documenting the information. When we first started completing this requirement, we did record the pressures as well, but changed it to only record the gpm. We do still take the static and residual readings to confirm system demand can be met. We use that information as our new test point and plug that into the calculations. We had one project that had the gpm, but didn't have a residual comparable to the hydrant flow test. A valve on the underground main was found to be partially closed causing the problem. So not required by the standard, but good information to compare to your calculations if you are performing the initial installation.
Reply
Ricardo
8/31/2026 08:39:00 am
For testing you need both. How else are you going to confirm the flow? The basic equations for hydraulic flow require pressure as one of the values used to determine the flow of a system, outlet or sprinkler. Simplified the equation is Q=k*Square root(p). Q being the flow, k is the derived K constant of the sprinkler and p being the pressure.
Reply
danefre
9/1/2026 08:40:42 am
While there’s certainly nothing wrong with recording the static/residual pressure during the test, you don’t need it to determine or confirm the flow.
Reply
Jack G
8/31/2026 01:09:53 pm
A forward flow test of the BFP has long been required by 25 fating back maybe to 2002.
Reply
Jack G
8/31/2026 03:43:06 pm
If you don’t record the pressures while you flow, I feel the use of the tests is like an extrapolation , you have a max and minimum flow and extrapolating between the two points without pressure readings is useless information for an AHJ.
Reply
JK
9/1/2026 03:26:39 am
Coming from the an AHJ side, UFGS 21 13 13 is clear about what must be recorded. The intent is to flow the calculated system demand flow and record the pressure drop across the backflow preventer. The recorded pressure drop must correspond with the backflow preventer manufacturer’s product data at the specified flow rate. This information is typically provided on a metal placard attached to the backflow preventer. The maintenance activity needs to know the expected pressure drop so it can be replicated during future testing. This provides a consistent reference point for verifying that the backflow preventer continues to operate as intended.
Reply