How should the new provisions in FMDS 2-0 (2025 Edition) regarding skylights in storage areas (sections 2.5.4.1.7 and 2.5.4.1.8) be correctly interpreted?
I have two cases based on the flowchart from the snippet below. In both scenarios, sprinklers will be required (even in the case highlighted in the green rectangle, which is optional). My question is: Should they be installed at the base of the skylights, at the same level as the surrounding ceiling-level sprinklers (similar to Option 2 for skylight protection in the 2023 edition of FMDS 2-0)? Or should they be installed inside the skylight, close to the highest point of the skylight (similar to Option 1 for skylight protection in the 2023 edition of FMDS 2-0)? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Pete H
3/4/2026 06:30:09 am
One of your pockets is less than 18" deep, so between the top and the bottom of the pocket, it really doesn't matter. It will cover heat collection in that 18" ceiling pocket. The advantage of option 1 is less worry about cold soldering adjacent sprinklers.
Reply
Anthony
3/4/2026 07:43:40 am
Put the sprinkler ~ 1 ft down from the top of glass. Use a 212°F sprinkler.
Reply
Ewelina
3/5/2026 03:17:12 am
In Poland, this is the most common configuration due to local regulations. I am referring to continuous skylights equipped with smoke vents, which is the case for the scenario mentioned above. These vents are also used for comfort ventilation (opening during non-fire events).
Reply
Anthony
3/5/2026 09:39:42 am
Very interesting, thank you for your insight. Leave a Reply. |