Is a flow switch required on the discharge side of the fire pump on the pipe before it exits the pump room?
We have an approved job that does not have a flow switch, and the fire marshal is requiring one. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
20 Comments
Pete H
12/9/2024 06:42:00 am
My immediate questions:
Reply
Glenn Berger
12/9/2024 08:09:39 am
My questions will be:
Reply
Casey Milhorn
12/9/2024 09:08:04 am
I believe NFPA 14 now requires this if you have standpipes/hose valves. From a practical perspective, 100% of the time provide a flow switch. I've heard too many stories about hose valves being opened up and/or leaks occurring and flooding stairwells, basements, and/or adjacent properties. If you are a contractor, I would go through the RFI process though if it isn't contractually required by the standard or design intent drawings/specs.
Reply
Franck
12/9/2024 09:08:35 am
The technical answer is no.
Reply
Anthony
12/9/2024 09:13:31 am
From a practical sense if the fire marshal is requiring it just install it that's not a fight worth fighting.
Reply
Dan Wilder
12/9/2024 09:58:10 am
I will disagree with this method of thinking all day. Is it a hill I'm dying on, maybe-maybe not but it will always be under protest with the GC & owner involved so I have a means to recoup costs.
Reply
Jesse
12/9/2024 11:42:02 am
I agree with Dan here. I'm never afraid to question the fire marshal and stand up for my position. I was one for a long time so I kind of have an inside track.
Dewayne Martinez
12/11/2024 07:57:22 am
I agree with Dan also. We have quite a few AHJ's that request some "wild things" during inspections. We politefully ask that they send us their requests in writing with the specific code reference so that we can send it along to the GC/Owner. Most of the times the issue just dies there.
Anthony
12/12/2024 03:40:24 pm
Dan, you're right, I'm wrong or at least I'm narrow in my view. I'm looking at this question as a design reviewer/engineer not as contractor or GC. I 100% agree if this is a post instillation comment then I'd fight it too.
Jack G
12/9/2024 09:52:43 am
I agree with Anthony on this one.
Reply
Jose R Figueroa
12/9/2024 10:31:22 am
Assuming the Fire Pump system is installed in accordance with FM DS3-7 or NFPA 20 (supporting standpipes, hydrants, fire hose stations, and sprinkler systems), the response to the query is NO.
Reply
Jack G
12/9/2024 10:39:32 am
I think the intent…..is to install an alarm “ on the system”. The system being “ the combined standpipe/ sprinkler system”.
Reply
Jose R Figueroa
12/9/2024 11:03:52 am
The alarm may not be needed in this situation and could lead to confusion. The fire pump controller is designed to automatically activate an alarm when the motor or diesel engine starts running, ensuring that any necessary action is taken promptly. Please refer to FM DS 3-7 or NFPA 20 for further guidance.
Reply
Jack G
12/9/2024 11:13:00 am
The text clearly shows a flow switch on the combined system. So argue the controller will signal this alarm. If the AHJ does not agree then bite the bullet and provide. The AHJ has the last word. If not shown on the contract documents ( which usually includes the clauses provide — per NFPA and AHJ ) you may be able to wiggle a change order. My opinion…..not.
Reply
Ronnie Morales
12/9/2024 11:14:22 am
Why not ask the AHJ to show you where the requirement is coming from? Then you can have a discussion if it's required or not.
Reply
Patrick Drumm
12/10/2024 07:33:46 am
I agree with Ronnie. It is always best to understand what code/section the AHJ is referencing.
Reply
Ronnie Morales
12/9/2024 11:35:35 am
Here is a requirement.
Reply
Jose R Figueroa
12/9/2024 12:40:43 pm
This response may not align with the Fire Marshal's requirements. In confined spaces where the visibility of water flow through relief valve piping is limited, a closed-type cone or V-Cone® differential pressure (DP) meter could be more appropriate. So, this is an entirely different issue.
Reply
J.H.
12/9/2024 12:12:51 pm
What is the exact wording of the write-up from the fire marshal?