Fittings Need a Listed Pressure to Meet Churn?

9/3/2025

7 Comments

 
We installed UL Listed grooved fittings with a rating up to 300 psi. The churn pressure of the fire pump is reaching 355 psi. The AHJ is asking for UL Listing or FM Approval to be above this pressure.

Is it mandatory under NFPA to have a UL Listing or FM Approval for the grooved fittings to cover the churn pressure, or is up to 300 psi acceptable?

What are our options here if we have to do anything?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Pete H
9/3/2025 07:42:23 am

The fittings need to be able to handle the pressure of the system, even at churn.

So if the fitting is only listed to 300 psi, you can't have 355 psi in the system. It can burst/leak/break the fitting.

Yes, NFPA does call this out.

Your options are likely a pressure regulating device or valve.

Reply
Glenn Berger
9/3/2025 08:15:30 am

I concur with Pete's responses. The use of a PRV may not be possible since a very high pressure fire pump was chosen. May need to reconsider this design.

My guess of the design conditions is that a significant high-rise building is being protected. It use to be the design procedure to provide additional fire pumps at an elevated level (with a possible water tank). This would reduce the pressure rating of the main pump(s).

Reply
Jesse
9/3/2025 08:46:09 am

Yeah, what Pete and glenn said. Defimitely don't want to temp fate there

Reply
Ken Thackery
9/3/2025 09:13:34 am

Victaulic 009V will get you 365 psi, we tested 009N in a high rise at 350psi and they leaked so we switched to the V. Change out the couplings and you will be good. It's not worth the liability or lawsuit if something fails and they find out the equipmemnt wasn't listed for that pressure.

Reply
Ryan Hinson
9/3/2025 12:59:59 pm

Churn pressure must be considered on all downstream components which will be exposed to that pressure. The manufacturer MAY have other higher working pressures. I suggest reaching out to them for such documentation... otherwise provide what the AHJ is asking for.

As an example, Gruvlok products submittals catalog states the following:
- "Pressures to 250 psi on cut or roll grooved pipe with a wall thickness of 0.25" or greater."
- "Working Pressure, End Load & Pipe End Separation Based on standard wall steel pipe with cut or roll grooves in accordance with Gruvlok specifications. See technical data section for design factors."
- "Pressure ratings of Gruvlok standard fittings conform to those of Fig. 7001 Gruvlok coupling."
~ Fig 7001 coupling states "Maximum Working Pressure Rating is for schedule 40 steel pipe. For light wall, stainless steel, aluminum and ISO pipe pressure ratings, please refer to the technical data section. Not for use on "EG" rolled or cut grooved pipe ends."

Just realized this inquiry is regarding grooved fittings after having already written my initial response below. As such, I'll just include anyways:

From a flanged fitting standpoint, the pressure rating of a given pipe/fitting component is based on the specific material from which it is made and the temperature at which the piped liquid will operate as well as the applicable ANSI/ASME fitting standard:

- The stated pressure ratings for grey/cast iron fittings are at steam temperature of 353°F per ANSI/ASME B16.1. For example, an ASTM A126 Class A cast iron fittings having ASME B16.1 Class 125 rating is rated for 125 psi at 353°F. At temperatures 150°F or less, size- and Class B compoonent-specific pressure ratings are 150 psi or higher. See Table 3-1.1 of ASME B16.1 (2020) for more information.

- For forged or cast pipe flanges and flanged fittings, ASME B16.5 (2025) Tables 2-1.1 through 2.1.19 (2-1.4C for weekest group materials), a Class 150 rated component is rated for a working pressure of 235 psi for temperatures up to 100°F.

- For Ductile iron fittings, a Class 150 rating has a rated working pressure of 250 psi at 100°F or less per ASME B16.42 (2021) Table 3-1.1C.

I suggest reaching to the fitting mfgr and asking what the 'working pressure' is for your fittings at whatever your maximum anticipated water temperature is (I would expect you are below 100°F).

I have found this document to be helpful: https://gaindustries.com/images/docs/whats-up-with-flanges-7-18-24776.pdf

Good luck!

Reply
Jack G
9/3/2025 04:24:05 pm

Manufacturers obviously “ test “ their products at higher pressures than what they get approved thru UL/FM, so they don’t get leakers at the rated pressures. Sprinkler heads at one point were tested at 500 psi for 30 seconds.
But the labeled pressure is what you need to go by.
I d take Ken’s advice and see what the fittings are rated for ( with the actual piping) and see if the couplings could give you the rating, like an 007 coupling.
A prv could be used but you would have to take into account the system design. I m thinking the system would not need the actual churn pressure.

Reply
Jack G
9/3/2025 04:34:46 pm

In the Philadelphia area I ve found that A&E s design systems with pumps as stand alone ( system design is satisfied with just the pump ) and not take into account the city pressure and flow. ( degregation of city supply with development ).
Some will spec a PLD fire pump to deal with the excess pressure however the pump is tested with the PLD feature off so the excess pressure has to be designed for ( testing) .
I don t agree with this concept but that’s what some engineers do.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT