MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Fireproofing for Column on Exterior of Exit Stair?

10/14/2024

7 Comments

 
This is a corner exit stair in a 2-story Type II-B building. There is 2-hr fire separation per client request (only 1-hr by code).

There's one column in the corner that only supports exterior precast walls and roof structure. Does it need to be fireproofed?

I would assume it doesn't. Any ideas? Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
7 Comments
Glenn Berger
10/14/2024 08:09:37 am

Some fireproofing might be required. Need to see full detailing on how fire separation is being planned.

Reply
Todd E Wyatt
10/14/2024 08:23:03 am

This column meets the definition of Primary Structural Frame …

PRIMARY STRUCTURAL FRAME. The primary structural frame shall include all of the following structural members:
1. The columns.
2. Structural members having direct connections to the columns, including girders, beams, trusses and spandrels.
3. Members of the floor construction and roof construction having direct connections to the columns.
4. Members that are essential to the vertical stability of the primary structural frame under gravity loading.

… and per the building’s Type of Construction (TC), the fire-resistance rating (FRR) would either be 1-Hour (II-A) or 0-Hrs (II-B).

If the building is II-A, the FRR protection could be any tested/listed assembly that includes “individual encasement protection by protecting it on all sides for the full column height” :

IBC-2021
Chapter 7 Fire and Smoke Protection Features
Section 704 Fire-Resistance Rating of Structural Members
704.2 Column Protection
Where columns are required to have protection to achieve a fire-resistance rating, the entire column shall be provided individual encasement protection by protecting it on all sides for the full column height, including connections to other structural members, with materials having the required fire-resistance rating. Where the column extends through a ceiling, the encasement protection shall be continuous from the top of the foundation or floor/ceiling assembly below through the ceiling space to the top of the column.
Exception: Columns that meet the limitations of Section 704.4.1.

II-A includes the following keynotes :

b. In all occupancies, heavy timber complying with Section 2304.11 shall be allowed for roof construction, including primary structural frame members, where a 1-hour or less fire-resistance rating is required.
c. Except in Group F-1, H, M and S-1 occupancies, fire protection of structural members in roof construction shall not be required, including protection of primary structural frame members, roof framing and decking where every part of the roof construction is 20 feet or more above any floor immediately below. Fire-retardant-treated wood members shall be allowed to be used for such unprotected members.

Even if your building meets the “C” exception not requiring FRR protection of this column, the Interior Exit Stairway’s (IES) would require a 1-Hour FRR assembly per the scoping Code (e.g. IBC-2021).

IBC-2021
Chapter 10 Means of Egress
Section 1023 Interior Exit Stairways and Ramps
1023.2 Construction
Enclosures for interior exit stairways and ramps shall be constructed as fire barriers in accordance with Section 707 or horizontal assemblies constructed in accordance with Section 711, or both. Interior exit stairway and ramp enclosures shall have a fire-resistance rating of not less than 2 hours where connecting four stories or more and not less than 1 hour where connecting less than four stories. The number of stories connected by the interior exit stairways or ramps shall include any basements, but not any mezzanines. Enclosures for interior exit stairways and ramps shall have a fire-resistance rating not less than the floor assembly penetrated, but need not exceed 2 hours.
Exceptions:
1. Interior exit stairways and ramps in Group I-3 occupancies in accordance with the provisions of Section 408.3.8.
2. Interior exit stairways within an atrium enclosed in accordance with Section 404.6.
3. Interior exit stairways in accordance with Section 510.2.

Reply
Todd E Wyatt
10/14/2024 04:19:28 pm

The fire-resistance rating (FRR) requirements for ALL columns (e.g. Primary Structure) are determined by the Type of Construction (TC) of the building : either 1-Hour for TC II-A or 0-Hrs for TC II-B.

The FRR protection of the Interior Exit Stairway (IES) ... if that is what it is ... is determined by IBC Chapter 7 & Chapter 10.

Just because columns are located in a 1-Hr FRR-protected IES does not make them compliant per the Type of Construction requirements.

Reply
O.P.
10/15/2024 09:34:59 am

Thanks for your comment! Like I said, this is a TC II-B building, so no fireproofing of primary structure required. The column is fully contained within a 2HR egress stair enclosure (only required to be 1 hr by code). Getting different answers so far from the forum (thanks to all!!!)

Reply
Todd E Wyatt
10/16/2024 08:28:50 am

Thanks for the clarification ... I apologize for missing the II-B Type of Construction (TC) in your initial explanation.

Based on that, the columns are NOT required to be FRR protected per the TC.

The vertical 2-Hr FRR assembly (e.g. 2-Hr Fire Barrier : 2FB) used to protect the IES is required to extend horizontally to the Exterior Walls. These 2FBs are required to either be self-supporting OR supported by a 2-Hr Horizontal Assembly (2HA) which could include the Floor Construction (FC) for the 2FBs on Story 02 (and slab-on-grade at Story 01). If the latter strategy is used, the FC at Story 02 would be required to match the FRR of the 2FBs it is supporting. Likewise, the Primary Structure (e.g. columns & beams) supporting the 2-Hr FC would also be required to be protected by 2-Hr assembly(s).

The extent of the 2-Hr protection of Story 02’s FC and its supporting structure should be coordinated with the AHJ since it is not prescriptive. Some AHJs will require the structural bay supporting the IES’s 2FBs to be protected with 2-Hr assemblies.


Dan Wilder
10/14/2024 08:35:58 am

Not a building code guy however...

The fire resistance of the member would fall into Section 704 (2021 IBC) and 704.2 and 704.3 specifically for "individual encasement" (several other sections like Table 601).

Also, Section 704.10 states that load-bearing structural members which are located within the exterior walls or on the outside of a building or structure shall be provided with the highest fire-resistance rating, as determined by Table 601, for the type of building element or exterior bearing wall, or by Table 602 based on the fire separation distance.

I also looked back through some of our previous projects and all those stairwells that had columns within were enclosed, either individually or within a stair shaft. Finally, in the illustration I see that the two other columns that share the same stair shaft are enclosed (either for constructability or due to the IBC requirements) which, if allowed to follow the column in question would also not require the rated enclosure.

Reply
Jack G
10/14/2024 10:18:17 am

It needs to be enclosed like the other columns.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT