Fire Wall or Fire Barrier to Avoid Spr. Retrofit?

3/18/2026

4 Comments

 
I have a project under the 2015 International Codes that is building onto an existing fitness center/gym. The existing building has an A-3 occupancy under 12,000 SF, but an occupant load over 300 people. The total fire area of this existing building is 22,300 SF. Also, the building is not sprinklered.

There is a new building going directly next to the existing building that will connect the two (they share a wall).

The new building is an aquatic center (pool and splashpad) with an A-3 occupancy under 12,000 SF, but an occupant load over 300 people. The total fire area of this new building is 13,000 SF.

The architect was originally trying to see if sprinklers could be removed from the scope (since there are none in the existing building), but based on the occupancy and square footage of the new building, sprinklers will be required (IBC 903.2.1.3). Since sprinklers are required in the new building, the architect is trying to determine what type of separation is required at the two buildings (fire partition, fire barrier, or fire wall) to avoid requiring retrofitting sprinklers in the existing building.

My take on it was to provide a "Fire Wall" to completely separate the buildings and not calling the existing plus new spaces a "single building" which could push us into requiring sprinklers throughout the existing building.

In addition, IBC 903.2.1 indicates that sprinklers "shall be provided throughout buildings and portions thereof used as Group A occupancies provided in this section" and sprinklers "shall be provided throughout the story where the fire area containing Group A-1, A-2, A-3, or A-4 is located and throughout all stories from the Group A occupancy to, and including, the levels of exit discharge serving the Group A occupancy." I then looked at the commentary on Group A-3 occupancies (903.2.1.3) which stated "an automatic sprinkler system is required throughout the fire area containing the Group A-3 occupancy, including the entire story where the Group A-3 occupancy is located..."

Based on 903.2.1 and the commentary on 903.2.1.3 it sounds like anything less than a "fire wall" used to completely separate the buildings, we would need to sprinkler the entire floor that the A-3 occupancy exists including the adjacent building since the are connected and share a wall. The architect's code consultant said I was wrong and that sprinklers are only required within the "fire area" and a "fire barrier" is sufficient.

In addition, IBC 903.1.1 indicates that if the code requires a building to be sprinklered then they are to be provided throughout. NFPA 13 (2019) also indicates that if a building is protected by a sprinkler system, then sprinklers are to be provided in all areas except for omissions indicated in the standard. I brought up this NFPA requirement and the code consultant said I was also wrong with this and that sprinklers are only limited to fire areas and aren't required to be installed throughout the building.

​I would appreciate any thoughts on this, thank you.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Anthony
3/18/2026 07:43:16 am

I think we need to be carful about using building code vs existing building code. Existing building code has language that would trigger upgrades to life safety systems based on the level of alteration. Last I looked its was and addition of 50%? that triggered the primary building to require a sprinkler system retrofit. (that was a B occupancy though)

Completely separating the buildings is a non trivial task but usually the preferred method when an addition calls for sprinklers.

Reply
Todd E Wyatt
3/18/2026 08:28:04 am

A Fire Wall (FW) would create separate buildings (existing and new) which would require evaluation of the Project per the currently adopted IBC edition.

A Fire Barrier (FB) between the Existing Building and the Addition would create Fire Areas requiring compliance of the Existing Building per the currently adopted IEBC edition to determine the Level of Alteration (1, 2, or 3) and compliance per the currently adopted IBC edition.

If the Alteration affects more than 50% of the total building area, it is classified as a Level 3 Alteration, which triggers stricter requirements for bringing the building, including sprinkler systems, into compliance.

The key terms are "Buildings" ... (2) Buildings if a FW is used ... and "Fire Areas" ... (2) Fire Areas if a FB is used.

Reply
Michael Knott
3/18/2026 01:02:56 pm

This was my exact thought process, Todd. Providing a fire wall would allow us to call them separate buildings and not running into the issue of calling it all one building and requiring the existing building to be brought up to code.

Reply
Darin
3/18/2026 05:27:34 pm

A fire wall does not create separate buildings for all code requirements. They create separate buildings for the purposes of allowable area, height, and type of construction requirements. Using these provisions to control other building features or elements such as means of egress, building systems or building utilities is not intended or implied by the provisions; e.g. fire sprinkler provisions. (see IBC 706.1 commentary)

IBC Chapter 5 is applicable to all new buildings as well as any existing structure that are to be enlarged. See IBC 501.1 (commentary)

What Jose describes below as a MFL is precisely what a IBC defined "fire wall" is required to do. See IBC 706




Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT