What are the requirements for fire suppression for a wood-fired pizza oven in a commercial application?
Does a wood-fired pizza oven require anything special, like a Type I hood would? If it does require some level of suppression - what's commonly provided? A high-temperature sprinkler on the adjacent fire sprinkler system, a feed from domestic water, or something else? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Anthony
8/19/2024 07:12:18 am
Ovens generally don't require any special sprinkler protection. If this is commercial like in a college kitchen, or specialty pizza restaurant it's just a piece of equipment. It should be treated as any other oven.
Reply
Pete H
8/19/2024 08:08:58 am
This sounds right to me. Only other worry I'd have is if they store wood for the oven in the kitchen to knock them out of OH1 and into OH2.... I don't see them having enough wood to be beyond miscellaneous storage.
Reply
Dave
8/21/2024 10:32:57 am
A garden hose is required for the wood storage, and a limit on wood quantity to be a single day supply.
Dan Wilder
8/19/2024 08:02:15 am
The only thing special we have provided in the past is 286Fº sprinklers in front of the open flame area, 200F° for the next ring.
Reply
Ricardo Gonzales Jr
8/19/2024 08:17:17 am
I would verify with Code. Last I understood, IF there is wood, as the name implies, the Kitchen Hood would need to be heavy Duty utilizing normal KH suppression. ICC does a full day class on Kitchen Hoods as there is a lot more to this topic than I originally thought.
Reply
Joe
8/19/2024 08:35:59 am
Any jurisdiction using the ICC family of codes...Solid Fuel Fired cooking indeed requires fire protection and a separate Type I hood. No sharing
Reply
Peter D.
8/19/2024 09:41:22 am
I respectfully disagree with some of the comments here. If you look in the IMC, the qualifier for kitchen equipment Type I or Type II hoods, is if the equipment creates grease-laden vapor. Olive oil, pepperoni, sausage, cheese, all make grease. Wood fired ovens can reach an internal temperature of 1300 F. I think the equipment should require a Type 1 hood and wet chemical extinguishing system, such as Ansul or Pyrochem.
Reply
Robert Morgan
8/19/2024 11:03:42 am
Many of these "wood-fired" ovens are listed for use without a type 1 hood or suppression. The reasoning is that the effluent burns at such a high rate they essentially consume the grease laden vapors. I have required a hood and suppression for open ovens, but I would check each appliance to determine their listings and follow that.
Reply
Jack G
8/19/2024 01:02:14 pm
I would consult the local code authorities.
Reply
Jesse
8/19/2024 02:51:16 pm
Generally, ovens are equipment and don't require protection. BUT, these are solid fiuel fired ovens and are treated different. I'd check with your AHJ
Reply
Russ walker
8/22/2024 01:29:24 pm
Thank you all for your comments, I have read them all and through my research prior to submitting my question I found a mixed bag of opinions as we see in your responses, and all of your points pro and con, so as AHJ I will evaluate the equipment try to come to a fair and safe decision that best meets the mechanical code in our jurisdiction. This is a great format for discussion.
Reply