A building will partially be a data center as part of a Group B Occupancy in the IBC.
Is a fire-resistance-rated separation required between the data halls and the offices? The data center area has accessory rooms such as a sprinkler riser room and a fiber cable entry, which are rated, but I'm looking at the data hall versus office specifically. Table 509 of the IBC doesn't mention anything about data center areas specifically. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Glenn Berger
7/30/2026 08:14:33 am
A complete code analysis is required to be completed to determine the answer to your question.
Reply
Todd Wyatt
7/30/2026 08:28:46 am
The (2) spaces/areas ... data halls and the offices ... would both be classified as Group B Business so Occupancy Classification (OC) separation would not be required.
Reply
Jocelyn
7/30/2026 08:29:21 am
The required separation depends entirely on what occupancy the data center is classified as, which is dependent on the equipment inside and which code you are using.
Reply
Dan Wilder
7/30/2026 08:45:45 am
**Not a Code Consultant***
Reply
Jack G
7/30/2026 09:24:03 am
So updating sprinkler design criteria does not permit omissions in fire walls ( just reduction in rating s increases allowable building area s for being sprinkered) as this is governed by the IBC chpt 7 and , section 508, govern structural compartmentalization, life safety, walls fire barriers life saftey egress separation and building area limitations..
Reply
Ricardo Gonzales
7/30/2026 10:02:32 am
My recommendation is the Arch/FLS team have a sit down with the Building & Fire Departments. I've seen multiple different classifications from the B to F1(factory?) all based upon the Li-ion batteries used. No consistency and the IBC '27 doesn't help much since they mention Li-ion and assorted chemistries, but not how the racks are set up nor the HMMAs recommendations. So you still have B, S1 and F1. FDs are still in the fearful mode and work to tell the Building Department they're wrong.
Reply
Steve F
7/30/2026 11:36:02 am
Separation is likely not required under IBC, assuming that accessory/incidental areas (fire pump, electrical room, generator/ UPS/ESS rooms, etc.) are separated, and both areas are B/F/S occupancies or other allowed non-separated occupancies per IBC Table 509.1. However, many data centers built to FMDS 5-32 or owner specific specifications which can result in separations that are more restrictive than IBC.
Reply
Flocode55
8/3/2026 08:18:04 am
NOT A DESIGNER: It has been my experience that some sort of separation may be required based upon type of fire suppression system and areas served. It may not be fire rated but usually HVAC systems, closing doors, isolate these areas. The method of separation is the designer's, owner's, insurance companies', methodology for risk management. I have seen fire/smoke barriers, to smoke barriers, to minimal amount of protection.
Reply