Where can I find guidance for fire flow for an outdoor lumberyard?
The IBC, Appendix B and C are for Buildings. It specifically says: "This appendix does not apply to structures other than buildings." Is there anything in the FM data sheets, or elsewhere? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Pete H
6/10/2025 06:20:38 am
NFPA 1 (2015 Ed) Chapter 31 is fire code for forest products.
Reply
Todd E Wyatt
6/10/2025 09:15:43 am
The scoping Code (e.g. IBC-2024) determines which Occupancy Classifications (OC) and/or special condition require an automatic sprinkler system (ASPS).
Reply
Todd E Wyatt
6/10/2025 09:16:56 am
CORRECTION ...
Reply
Janet Washburn
6/10/2025 01:41:07 pm
He's not asking if fire sprinklers are required. He's asking how he determines the needed fire flow (NFF). Fire flow is required to be calculated for firefighting purposes only. This is so the firefighters have the required amount of water to put out a fire. Nothing to do with fire sprinklers in that sense.
Brett
6/10/2025 09:18:34 am
The only time I've come across something like this was in a rural area with no water supply, so NFPA 1142 was applicable. I calculated the minimum water supply requirement pulling from a pond and draft hydrant for a few adjacent structures. Does NFPA 1142 apply to your situation? Is it adopted by your local code?
Reply
James E Art Fire Protection Engineer (FPE)
6/10/2025 03:09:42 pm
Thanks, I appreciate. BOATS?
Reply