Is it okay to design a fire protection system for a building using street pressure for the lower garage dry-pipe system, and using a fire pump for the upper floors when required?
If so, does NFPA 13 have a diagram for this? Also, how is the system piped to avoid starving the street pressure system when the fire pump engages? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Anthony
1/30/2025 08:05:15 am
This is perfectly fine as long as the FDC is properly connected to all systems.
Reply
Anthony
1/30/2025 08:22:35 am
Reply
Christopher Nelson
1/30/2025 08:07:22 am
You only account for one fire at a time.
Reply
Franck
1/30/2025 08:10:43 am
Do not forget to provide backflow preventer between the areas fed by the city water supply only and the areas fed by the booster pump (to avoid too much pressure for the lower garage protection areas).
Reply
James E Art Fire Protection Engineer (FPE)
1/30/2025 02:53:25 pm
Terminology and Costs. Requiring BACKFLOWs is Prohibited in Ca.
Reply
Jay
1/30/2025 03:23:59 pm
Is that correct? Backflow preventers are not permitted to be installed on fire sprinkler systems?
Jesse
1/30/2025 04:36:15 pm
I'm not sure I'm on board with this. Indeed, NFPA 13 doesn't require a backflow preventer. This is derived from plumbing code as a means to protect the water supply from contaminant.
Anthony
1/31/2025 08:23:52 am
Isn't it Cal Berkly that certifies backflow preventers?
Glenn Berger
1/30/2025 08:24:50 am
It is perfectly acceptable to provide a fire pump for upper floors and use city pressure only for lower floors.
Reply
Dan Wilder
1/30/2025 08:38:26 am
We do it, at rare times, to avoid the over-pressure issues but it has some draw backs...it is a case-by-case basis.
Reply
Jack G
1/30/2025 04:08:51 pm
Agree mostly with above comments.