I have a 115,ooo sq ft warehouse with a monitored sprinkler system. There is a pump room 200 feet away that has the FACP. The main water supply enters the building, then has three separate risers labeled as system 1, system 2, and system 3.
Is there a fire code that requires the building to have signage on the exterior of the structure indicating where Zone 1, 2, or 3 is? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Chad
1/5/2026 08:09:16 am
No there is not. That is what preplans are for.
Reply
Jeff Humphrey
1/5/2026 08:12:17 am
Thank you!
Reply
Jesse
1/5/2026 08:11:13 am
Happy New Year.
Reply
Pete H
1/5/2026 08:12:39 am
No requirement for exterior.
Reply
Dave L.
1/5/2026 10:39:36 am
FYI, the 2025 edition of NFPA introduces the requirement for a Documentation Cabinet (16.11.1.3).
Reply
Pete H
1/5/2026 01:14:53 pm
Thank you. Good to know.
Glenn Berger
1/5/2026 08:37:37 am
The previous responses are spot on. No national code requirement.
Reply
Jack G
1/5/2026 10:36:07 am
Agree. Just because it’s not required doesn’t mean
Reply