In NFPA 101, is a solid riser and a solid tread required for an Exit Stair?
See the image below that is metal tread but wouldn't have solid risers. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Todd E Wyatt
8/22/2024 08:20:22 am
The Means of Egress component shown appears to be an Alternating Tread Device (ATD) and not a Stair.
Reply
Todd E Wyatt
8/22/2024 08:21:05 am
NFPA 101-2012
Reply
Todd E Wyatt
8/22/2024 08:21:38 am
Enhanced Content
Brett
8/22/2024 09:05:32 am
The picture provided is not an alternate tread device. Here is what an ATD looks like.
Todd E Wyatt
8/22/2024 04:26:00 pm
CORRECTION
Reply
Todd E Wyatt
8/22/2024 08:33:55 am
Solid risers in stairs (stairways) are not required per NFPA 101-2012 but are per IBC :
Reply
Jack G
8/22/2024 08:34:59 am
Todd says it all. Agree!
Reply
Brett
8/22/2024 09:15:43 am
One thing to consider is if the stairs are located on the exterior of the building you must consider height and the requirement for a visual barrier.