MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Evaluate Water Hammer on Existing System?

1/17/2025

4 Comments

 
I'm working on a project in an existing 7-story building with an existing 500 gpm 70 psi fire pump.

We are installing a new 4-story riser outside the pump room, and a question of water hammer/surge protection has come up. The existing equipment does not indicate any special considerations for this.

Most (not all) zone valve assemblies incorporate pressure relief valves, and all new zones will have them, as well. Hydrant test static was 65psi.

In general, what conditions would prompt you to consider the possibility of water hammer or pressure surge being an issue?

How do you go about evaluating this, if it is a potential issue?

Thanks in advance.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Dan Wilder
1/17/2025 07:55:41 am

There should not be any issue....until there is an issue. You can show the current status by putting on a digital pressure recorder on the supply side of the incoming line for a couple days to see if there are any wild swings.

A majority of the system sits behind check valves (or should) so any start of a hammer will be dissipated from within individual zones and generally non-existent (unless you've got quarter turn valves that people are slamming shut, then those should be changed out).

I have seen hammer issues when jockey pumps are oversized...we found out the hard way when a project pump replacement started having issues and checking the data plate on the JP was towards the end of our diagnostic efforts (added PRV's to systems that did not have them, retested check valves that the existing ITM company said had passed that did not, added check valves on risers that only had butterfly valves as this was a multi-zone property).....changed the JP and everything came back to a normal condition...lesson learned!

Other times had issues when they were adjacent to car washes, typically 1-3 tap laterals away from the supply to the car wash were the problem buildings, and those were almost always smaller individual stand alone's like banks or medical offices.

Reply
Glenn Berger
1/17/2025 08:42:42 am

Water hammer should not be an issue except potentially at pressurization of the system. If it does occur you need to look for elevation changes in the piping network where air pockets may be formed. The other potential scenario is where a check valve is not seated correctly.

Since you have a pump on your system - if the pump is cycling then there is something that needs investigating.

Reply
Jack G
1/17/2025 09:21:47 am

Water hammer in a piping system is a large banging or knocking sound when the flow of water is stopped or change direction suddenly. It’s caused by a pressure surge, or shock wave that travels thru the pipe at the speed of sound ( as I learned in my college fluid mechanics course - Che eng) .
What causes it— a valve closing too quickly, a sudden stop by a jockey, Fire pumps , and a pressure wave resonates in the piping system.
The effects could be damage to the pipe and fittings, pumps and motors, can cause pressure spikes that are much higher than the pressure rating of the system, and could cause a pipe to burst.
How to correct for it ?
First I would install air relief valves at the top of each standpipe, along with a pressure relief valve set say at 175/psi— or psi rating of the system, , and at the highest point on each floor an air relief, ( are checked off from the standpipe systems ( required on wet systems - and pressure reliefs on system side of check) — the relief valve at the riser could release the spiked pressure but could leave trapped air in the system — causing a sponging and quick stop )
There are water hammer arrestors that are made for the fire pump discharge that could be added.
Make sure that the jockey pump settings are per NFPA 20. ( in a high rise especially the contractor sets the up on and off pressures lower due to elevation of the building) if the jockey pump comes on at a “ lower pressure than “ churn plus 5 psi” and off at say churn plus 10 or 15, it could cause a shock wave when it suddenly stops . ( longer run time.
In my opinion, the air relief valves along with pressure release valves will curtail water hammer.

Reply
Anthony
1/20/2025 07:48:22 am

Check out a wafer check specifically the Kennedy valve fig 806 is listed as a water hammer dampening device. Might be applicable here.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT