I have a quick question about estimating the pressure requirements for an automatic wet sprinkler system during the initial design phase.
Qm = d X (Area per Sprinkler) = (0.15) X (130sqft) = 19.5 gpm Estimated Total Flow (ETF) = Qm X N X F plus hose demand = (19.5 gpm) X (12 sprinklers) X (1.30 for spray pattern overage) + 250 gpm (Outside Hose Stream) = 554.2 gpm Minimum pressure needed for the system. = (19.5gpm/5.6K) = 12.13 psi for the most demanding sprinkler + another 20-35 psi for potential friction loss throughout the reference. The total estimated pressure needed would be 47.13 psi, not factoring in elevation change. The 20-35 psi for potential friction loss is an engineering judgement based on experience. What is the recommended potential friction loss for an initial design phase, and where would it be referenced at? I need to reference the source of recommended potential friction loss for the project. SFPE, NFPA or etc? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Anthony
11/13/2025 08:37:23 am
Generally I use remote area size * demand +20% + HA to estimate. (sqft x gpm/sqft *1.2+250) Ex: 1500sqft x 0.15 gpm/sqft * 1.2 = 270 + 250 = 520 gpm. Looking at induvial sprinklers at the estimating phase can lead to trouble later and takes too long.
Reply
Jack G
11/13/2025 08:52:51 am
They may be referring to SFPE5th edition chapter 41. " Hydraulics ".
Reply
Wes
11/13/2025 09:22:32 am
I would express some caution to using a "rule of thumb" for system friction loss as a blanket value. Some systems could be very long (long pipe runs), have unique pipe types (CPVC vs steel vs copper), vary in system type (dry, wet, preaction), and vary in arrangement (tree, loop, grid).
Reply
Jesse
11/13/2025 02:47:37 pm
Gotta garee with Wes here. I have this conversation with architects a lot when they ask us to estimate FL. The consultants "rough numbers' are no match for a calculation.
Reply
Jack G
11/13/2025 02:57:57 pm
The “ rules of thumb “ is used to calculate the pressure left after all the critical losses and divide that by the footage of pipe to the remote area from the supply .
Reply