|
Would ESFR K25.2 be permitted to be installed on a single interlock pre-action system?
I have a system conversion that is currently a gridded warehouse with K25.2 ESFR pendents that the client wants to convert to single interlock. The system will be converted to not be gridded anymore, but I am not seeing any clear information on whether the existing ESFR can remain. If we were to remove the sprinklers, it would now dive into possible in-racks to protect the class IV storage. Warehouse is 35ft max height, bar joist. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Pete H
4/24/2026 06:14:02 am
Depends if the listing states that it's for wet systems only. Some will list that, they'd be right out. Some don't mention it.
Reply
Brett
4/24/2026 07:50:36 am
That pdf is from 2005 so I wouldn't recommend referencing it without contacting Viking. The listing for the VK510 says wet systems only.
Reply
Anthony
4/24/2026 08:48:31 am
they tyco/JCI Quell / VanQuish system is used in freezer applications if you're asking about a dry type system.
Reply
Jonathan Griffin
4/24/2026 09:22:29 am
If using NFPA 13 (2019 or better), Pendent & Sidewall sprinklers can be used (w/return bends) where in an area maintained above 40'f. This may address the orientation issue... ESFR sprinklers are listed for Wet-only as far as I can determine (there may be one out there, I just don't see it). Using ESFR sprinklers that are also listed for non-storage use may be a way to go (K14 & K16.8 are available in this activation (CDMA - ELO) mode.
Reply
Glenn Berger
4/24/2026 09:31:49 am
Check the listing of the proposed mfg. and make sure the applicable ones get installed.
Reply
danefre
4/24/2026 01:23:55 pm
ESFR is out of the question, no listed product available.
Reply
John D
4/24/2026 03:53:18 pm
Wouldn't it be possible for Table 24.3.1 to be utilized since in some cases you can consider a single interlock to be a wet system?
Reply
danefre
4/27/2026 10:08:08 am
Single interlock can't be considered a wet system. The only connection is that you are not required to increase your remote area for SI when using the Density/Area method.
NK
4/24/2026 06:27:40 pm
There's not enough information here regarding commodity classification and proposed storage height, but here's an idea.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Sept '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
October 2026
PE PREP SERIES |
RSS Feed
