MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Elevator Hoistway Be a 'Convenience Opening'?

7/5/2024

3 Comments

 
Can an elevator hoistway connecting two adjacent stories be considered a "convenience opening" and avoid a fire resistance rating altogether based on NFPA 5000?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
Todd E Wyatt
7/5/2024 10:46:06 am

NFPA 5000 is an Occupancy Classification (OC) based Code. Chapters 1-15 & 32-56 include general requirements and “Chapters 15 through 31 and 33 through 34” include additional requirements and restrictions based on the OC(s) in the building and/or a special condition (e.g. High Rise Buildings). A “convenience Opening” (CO) may be permitted in (1) OC (e.g. New Business) but may not for another OC (Health Care).

NFPA 5000 - 2023 8.12.5.1 includes (6) conditions where an “unenclosed vertical openings not concealed within the building construction shall be permitted.”

8.12 Vertical Openings.
8.12.1 General.
8.12.1.1
Every floor that separates stories in a building shall meet the following criteria:
1) It shall be constructed as a smoke barrier in accordance with Section 8.11.
2) It shall be permitted to have openings as described by 8.12.2, 8.12.3, 8.12.4, 8.12.5, or Chapters 15 through 31 and 33 through 34.
8.12.5 Convenience Openings.
8.12.5.1
Where permitted by Chapters 15 through 31 and 33 through 34, unenclosed vertical openings not concealed within the building construction shall be permitted as follows:
1) Such openings shall connect not more than two adjacent stories (one floor pierced only).
2) Such openings shall be separated from unprotected vertical openings serving other floors by a barrier complying with 8.6.5.
3) Such openings shall be separated from corridors.
4) Such openings shall be separated from other fire or smoke compartments on the same floor.
5) Such openings shall be separated from the corridor referenced in 8.12.5.1(3) by a smoke partition, unless Chapters 15 through 31 and 33 through 34 require the corridor to have a fire resistance rating.
6) Such openings shall not serve as a required means of egress.

If the elevator hoistway meets all (6) conditions and if the building’s Occupancy Classification(s) permit Convenience Openings, then it is permissible for this elevator hoistway (connecting (2) stories) to NOT be protected by a fire-resistant rated (FRR) assembly.

Most jurisdictions do not adopt only (1) Code … chances are, the building will also have to meet an ICC Code. IBC-2021 addresses “Convenience Openings” as “Two-Story Openings” with similar (6) conditions :

Chapter 7 Fire and Smoke Protection Features
Section 712 Vertical Openings
712.1.9 Two-Story Openings
In other than Groups I-2 and I-3, a vertical opening that is not used as one of the applications specified in this section shall be permitted if the opening complies with all of the following items:
1) Does not connect more than two stories.
2) Does not penetrate a horizontal assembly that separates fire areas or smoke barriers that separate smoke compartments.
3) Is not concealed within the construction of a wall or a floor/ceiling assembly.
4) Is not open to a corridor in Group I and R occupancies.
5) Is not open to a corridor on nonsprinklered floors.
6) Is separated from floor openings and air transfer openings serving other floors by construction conforming to required shaft enclosures.

Reply
Jack G
7/5/2024 02:34:00 pm

Agree with Todd.
Must be protected from smoke transfer, floor to floor.
Hoistway to have a smoke detector within 2 feet of sprinkler.
IBC calls for 1 hr shaft for 2 story elevators.
IRC the same.
If elevator involves hydraulic fluid, must have a rated enclosure and fire sprinklers.
All depends on specifics of the build.
Should reference Meyer fire “ elevator” cheat sheet from the tool box.

Reply
Panos
7/6/2024 01:06:02 am

Thank you both for replying!

The fact is that we finally reached a decision based on a few other things.

After speaking with a friend who was a member of the NFPA technical committee, I requested a clarification from NFPA’s current technical committee. Their reply:

“For assembly occupancies, please see 16.3.1 for requirements, which reference 8.12, unless permitted by one of the four parenthetical requirements. In 8.12.5. I read that convenience openings are generally stairs that offer convenience for occupants to use rather than traversing to exits to move between two floors. Note 8.12.5.1 and its six parenthetical requirements. Convenience openings cannot connect more than two adjacent stories, with one floor pierced, require specific protections, and do not serve as a required means of egress.

Please see 8.12.6 for service openings regarding elevators, which provides specific requirements, including the number of cars per 812.6.4.”

It seems that the intent of the NFPA code art. 8.12.5 for convenience openings had stairs in mind. This is the reason for the requirement “not concealed within the building construction”. An elevator shaft opening between two stories is concealed from bystanders so we cannot use 8.12.5 to omit rated hoistways.

However, the NFPA 16.3.1 reference goes

“16.3.1 Protection of Vertical Openings.
Any vertical opening shall be enclosed or protected in accordance with Section 8.12, unless
(…)
(3)Assembly occupancies protected by an approved, electrically supervised automatic sprinkler system in accordance with Section 55.3 shall be permitted to have unprotected vertical openings between any two adjacent floors, provided that such openings are separated from unprotected vertical openings serving other floors by a barrier complying with 8.12.1.5.”

Our case is a fully sprinklered assembly occupancy, with no unprotected vertical openings in the same fire compartment, so yes, an elevator can have a non rated hoistway for two stories only if NFPA 5000 not applicable and not IBC.


Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Aug '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT