NFPA 2001, Standard on Clean Agent Fire Extinguishing Systems now require an egress time study to show that the design limits exposure to halocarbon agents is no longer than 5 minutes, like FK-5-1-12 (NOVEC 1230), HFC-227ea (FM 200).
This comes from 2018 Edition Section 1.5.14, 2020 Edition Section 4.3.4, and 2022 Edition Section 4.3.4. Exposure time for inert gas agents will depend on the oxygen levels within the space or room. Concentration below 43 percent shall be permitted where exposure is no longer than 5 minutes. Concentration between 43 and 52 percent shall be permitted where exposure is no longer than 3 minutes. The annex of NFPA 2001 tells us to review the NFPA Handbook and the SFPE Handbook for more information. Is anyone doing these calculations, and if so, what exit flow, movement speed, and reaction time would you consider appropriate for spaces using these systems? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Jesse
4/9/2025 09:18:38 am
I have to preface my response with these comments are mine, and I'm not speaking for the NFPA 2001 technical committee, etc etc etc.
Reply
Joe
4/9/2025 10:52:09 am
Several factors must be reviewed to complete the time egress study this including the
Reply
Chris Nelson
4/11/2025 08:30:45 am
This is backwards. RSET should be less than ASET.
Reply
Chad
4/9/2025 11:32:46 am
Are there rooms that are large enough where RSET would ever be greater than 3 or 5 minutes where there is an agent system? I am looking for an example so I can wrap my brain around why you would need to perform the calc?
Reply
Joe
4/9/2025 01:20:46 pm
Data center and other spaces like them can take that long.
Reply
Ricardo Gonzales Jr
4/9/2025 03:13:54 pm
When looking at the concentrations, be sure not to confuse the agent concentration with O2 concentration. O2 is maxed out at 20.6% at sea level and holds fairly well as elevation increases. It's agent concentration that changes as air pressure is lessened. i.e. at sea level the O2 pressure is 14.7psi, but at 6,000 feet the pressure drops to 11.8psi. O2 is still 20.6% makeup but of only 11.8 psi. Takes less agent to get the same % of concentration in the room. When atmosphere pressure gets below a certain point, our bodies no longer can absorb O2 out of the air. It's the agent exposure that is of concern.
Reply