Effectiveness of Sprinklers Not Under A Surface?

8/7/2020

7 Comments

 
I am looking for opinions on the effectiveness and likelihood of a timely operation of sealed sprinklers in open spaces where they are not installed below ceilings or obstructions.

For example, operation of sprinkler under open-grate platforms, or where used as pilot heads around external transformers. Many thanks.

​​​​​​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments
Paul
8/7/2020 10:22:22 am

Without a surface (for heat to collect) a sprinkler head would be very ineffective (in general). The heads would only fuse if it were directly above an open flame. It does have it's specific use. In the case where the idea is that it is positioned above an open flame as mentioned, usually in conjunction with an overhead system. (Flue spaces for rack storage, open grates, etc)

Reply
Phil W
8/9/2020 01:17:59 pm

Many thanks for the reply. It bears out my own thoughts really; I guess a head will operate at it's designated temperature, but that temperature would necessitate the head to be sufficiently close to the heat source. I've had conversations with water mist nozzle manufacturers previously on the same subject and they described specific nozzle testing where the distance from a soffit was increased; naturally they saw a delay in the operating time of that nozzle with the increasing distance.

Reply
DL
8/7/2020 10:32:25 am

Paul is right on. Some designers might remember how it was common practice to add "heat collectors" (a.k.a. "pie tins") or square pieces of sheetmetal above sprinklers (such as in a new tenant space prior to ceilings being installed), thinking they would collect heat around individual sprinklers, or even thinking an intermediate-level sprinkler does the same thing. But heat collectors was never an acceptable method and is now specifically prohibited in NFPA #13 as they have been proven to be virtually ineffective.

Reply
Pete D.
8/7/2020 02:16:37 pm

For the applications you described, a deluge system activated my smoke or heat detection would be the preferred fully functional fire protection system to design.

Reply
Franck
8/10/2020 03:22:43 am

As indicated above, sprinkler heads need a "real" ceiling to activate the thermal sensible element with the collection of heat.
If the heads are located too far from the ceiling, this will be, in the best case, delayed with activation of more heads and possible overtax of your system, in the worst case, result in no activation of the heads.
There is no evidence of efficiency with metallic plates, even with 2 ft x 2 ft plates.

A study performed in 1990 (“A Study of the Utility of Heat Collectors in Reducing the Response Time of Automatic Fire Sprinklers Located in Production Modules of Building 707,” prepared for the U.S. Department of Energy Rocky Flats Plant by Hughes Associates, Inc. (HAI)) stated the following:
• Heat collectors with the edges turned down around the side produced a dead air space and the sprinklers had longer response times than sprinklers with a flat heat collector
• The heat collector must be in the plume to be effective. If the centerline of the fire is more than 1 to 2 feet from the edge of a flat heat collector, a standard-response sprinkler may take longer to respond, regardless of its thermal sensitivity.
• If a fire is midway between two sprinklers, the sprinklers may not respond at all (regardless of the size of the heat collector) because the sprinklers are not exposed to the convective heat flow of the ceiling jet.
• Quick-response sprinklers activate more quickly than standard-response sprinklers only if the fire was directly underneath the heat collector.

See also Minnesota State Fire Marshal "Quick Response" April 2011 issue (https://dps.mn.gov/divisions/sfm/programs-services/Documents/Quick%20Response%20Newleter/QR0411HeatCollector.pdf)

There are anyway some exceptions to this rule.

1. Heads installed sometimes below open grate platform such as in a turbine hall. There are not provided to activate alone, but installed to provide an additional protection in case of 3 dimensional fire (which could be the case with oil flowing from the turbine deck down to the ground) - See FM data sheet 7-101 - Steam Turbines and Electric Generators for more details. NFPA 850 and 804 are less self explanatory.
2. Heads installed as pilot sprinkler system. The aim is not to activate all the heads in a given area, but to activate at least one head to operate the deluge valve. There is some chances that at least one head will be installed directly in the fire plume and thus activate your system.
3. New sprinkler heads are under development, called Thermal Radiation Activated Sprinklers or RAS (studies performed by Factory Mutual) and they may partially compensate the absence of ceiling.

Reply
Phil W
8/14/2020 10:11:08 am

Thanks for your compehenive reply, very interesting.

Reply
Dale Morris
8/10/2020 10:52:30 am

Just had this real life scenario involving cable trays that are 4 feet wide. In some areas, where the cables in the cable tray exit the electric room, the trays are rather packed, so the sprinkler is more likely to activate, with the cables serving as that "hard' surface. But towards the end of the run, the cable trays are still 4 feet, but do not have much cable in them, and so they are more open than filled. We still opted to provide sprinklers under there, as we know down the road, the intent is for more equipment to come on board, and the trays will become more full as the years go by. The GC showed on a sketch a pendant sprinkler next to the tray, and I told him it had to go under. He asked about those heat collectors, and I had to tell him not allowed.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Aug '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT