|
NFPA 72 (2016) Section 17.7.5.3 says a duct smoke detector is required in the supply air duct; on the other hand, the IMC (2020) Section 606.2.1 says a duct smoke detector is required in the return air duct.
Which should I follow? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Glenn Berger
11/25/2024 08:26:02 am
All depends on what codes are applicable to the project. I have had many projects where detectors are provided in compliance with both documents.
Reply
Nic J
11/25/2024 08:28:43 am
This should come down to what code/standard is applicable for the installation of the HVAC equipment (NFPA 90A vs IMC).
Reply
Dave
11/25/2024 03:03:39 pm
My in-house alarm expert agrees with ^^Nick^^
Reply
M. Newell
11/25/2024 08:28:57 am
In the 2025 edition of 72 it changed the language to say:
Reply
Ricardo Gonzales Jr
11/25/2024 10:20:41 am
Code 1st meaning the IMC to be followed. But then also 72. Note when i.e. cfm volume. They are different and apply accordingly. Most times it's 2,000 cfm for the supply side and 15k cfm for the return. And then IF it's a combined return system then on each area the air comes from. If you have a copy of the IMC with comment and NFPA 72 with comments. They make it fairly clear when to add the duct detectors to the building.
Reply
Jack G
11/25/2024 10:43:29 am
Since both are connected to some sort of air handler, which in the event of a unit fire could propagate smoke, or in a building fire— distribute smoke I would lobby for both supply and return.
Reply
Brett
11/25/2024 10:46:33 am
What codes are you following? Is it a DoD project?
Reply
chad
11/25/2024 02:53:31 pm
There are plenty of State and LAHJ's that have adopted and enforce both, there is no conflict, you simply enforce the more stringent parts of each one, ie like Pete said "both"
Reply
Smith Choi
11/26/2024 09:49:56 am
Usually, Code triumph the standard. IMC took the precedence when in conflict with NFPA.
Reply
KFITZ
12/2/2024 02:36:16 pm
Applicability of NFPA 90A (as referenced by NFPA 72) and IMC is dependent on the prevailing building code requiring a fire alarm system.
Reply
Ivan J. Humberson
12/26/2024 10:48:11 am
You should check with the AHJ. In the jurisdiction from which I recently retired, both NFPA and IBC/IMC need to be met, so we amended the IMC to require duct detection on the return side for systems between 2,000 and 15,000 cfm. Without such an amendment, for jurisdictions requiring compliance with both NFPA and ICC codes, one would have to install duct detection on both supply and return for all systems over 2,000 cfm. We felt that was not necessary, hence the amendment.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop July '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
August 2026
PE PREP SERIES |
RSS Feed
