Do dual electrical feeds from two separate sources (same service provider, two different substations) with a UPS storage battery system that will support full load for 4+ hours meet the requirements for fire alarm secondary power?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Chad
6/5/2025 07:23:22 am
You need a generator if batteries are not calc'ed for 24 hours.
Reply
Glenn Berger
6/5/2025 08:20:55 am
In the 2025 version of NFPA 72, Section 10.6 is applicable. This chapter has expanded greatly over the last few versions. I think that the answer to your question is -- maybe.
Reply
Todd E Wyatt
6/5/2025 08:40:03 am
The appropriate edition of NFPA 72 is determined by the scoping Code ... typically the IBC.
Reply
Ricardo Gonzales Jr
6/5/2025 09:07:16 am
My opinion. No.
Reply
Jose Figueroa
6/5/2025 10:23:42 am
I wanted to say “no”, etc. All answers align.
Reply
Neil Chadwick
6/5/2025 10:28:37 am
Thank you for the replies! We tend to agree and are still requiring the 24-hr battery backup