Dry Sidewall Sprinkler That Throws 23-ft?

11/21/2025

10 Comments

 
We are designing a project that has a porch area (approximately 88-ft long x 23-ft deep) at grade with occupied enclosed building space above it (the building overhangs the porch by 23-ft).

To avoid a costly dry-pipe system for this area, the CM is looking to serve this area from dry sidewalls connected to the buildings automatic wet sprinkler system.

Is anyone aware of any dry sidewall heads (exposed or concealed) for this application that can throw 23-ft?

​The building will have a fire pump so the extra pressure would not be an issue. Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Pete H
11/21/2025 06:11:17 am

If it's light hazard the Reliable DH80 Dry EC can throw up to 28'-0"...

But it's 14'-0" around it in either direction on the side (total 28'-0") and 14'-0" in front of the sidewall. Still might work depending on how the walls are shaped. Other corridor sprinklers would be the same.

Other than that if it is residential: The reliable KRes58 HSWX (5.8K RA3593) does do 14' x 26'-0" (Or 16'-0" x 24'-0") but is a residential sprinkler. So if that's not your occupancy, you might have to clear it with an AHJ due to lack of options, but the AHJ would still be right to say "No you can't use a residential sprinkler in a non-residential space"

Reply
Dan Wilder link
11/21/2025 07:35:20 am

I don't know of any commercial dry barrel sidewalls that will spray over 20'. Any option to have a heated soffit built for the first 3'?

If not, check out A9.3.19.1 (2025, 2022. 2019) for a possible clarification as to how far the sprinkler protection is "intended" to spray with the outside support columns being that line, and any extension less than 4' beyond should not be considered for protection. Then get your AHJ to buy off on the intent.

Soffit option similar to this previous blog

https://www.meyerfire.com/blog/category/detail-critique

Reply
Anthony
11/21/2025 07:58:41 am

It think dan is right, the soffit is the "easiest" option from a sprinkler stand point. Maybe be careful if this is in an area that will experience significate freezing. That soffit will need to ensure it's part of the heat envelope of the building with plenty of internal heat exchange (pocket vents). It can't just be a box thrown on the side of the building.

With the occupied over head area is there a wall or pocket you can drop down in the center of that area? Possible to strategically place several dry EC pendants?

Reply
Chad
11/21/2025 08:03:33 am

Yes, see Joe's post at that link. Best option if possible.

Reply
Connor Ross
11/21/2025 09:20:57 am

My interpretation is that A.9.3.19.1 addresses obstruction rules and not required throw distance.

“
A.9.3.19.1 
Sprinkler protection under exterior projections should not be required to spray beyond the support beam on the exterior edge of the exterior projection as long as the maximum distance from the interior edge of support beam to the exterior edge of the projection does not exceed 4 ft (1.2 m). An additional line of sprinklers on the exterior edge is not required due to obstruction rules. This is considered a reasonable level of protection because sprinklers are located between the structure and the exterior edge. See Figure A.‍9.3.19.1.
“

The wording states “beam” and not “column” and the accompanying figure A.9.3.19.1 shows a horizontal structural member near the edge of the exterior projection. The figure notes that additional *sprinklers* are not required past the beam, not that sprinkler *coverage* is not required past the beam.

In the strictest interpretation, the sprinkler must still be capable of spraying the distance to the exterior edge, but the obstruction created by beams at the ceiling can be disregarded in terms of sprinkler obstruction rules which would otherwise require additional sprinklers to satisfy.

Looking at it practically, a beam that is deep enough to be considered an obstruction at ~20 ft away from the wall will likely inhibit the sprinkler spray from reaching its full coverage length regardless. One could make the argument that it doesn’t matter how far a sprinkler can spray if the water is never going to get there anyway.

Reply
Dan Wilder link
11/21/2025 12:26:22 pm

Yes, I agree with your interpretation for implied floor coverage for the sidewall but also one of the few places where exterior protection has exceptions. Using a residential sidewall may be outside of its listing (the OP did say porch not canopy, so Residential may still be on the table), providing the soffit may not be an option, and no protection may also be out of the option list. Tough spot all around.

Todd E Wyatt
11/21/2025 08:22:10 am

See "Extending Dry Sidewall Reach Just Beyond 20-ft" (https://www.meyerfire.com/blog/extending-dry-sidewall-reach-just-beyond-20-ft) ... otherwise, an extended-coverage sprinkler such as Reliable Model DH56 can cover up to 28-FT.

Reply
Dave
11/21/2025 11:46:06 am

To be clear, the greatest throw of the Reliable DH56 and DH80 is side-to-side (14' each way) not outward from the wall on which they are installed. I assume the structure is combustible construction? If NON-combustible, the occupied space above isn't necessarily a trigger for requiring sprinklers, although the handbook commentary has gone back and forth on this and some AHJ’s require it. Non-combustible might also allow the exit corridor exception of 9.2.3.3. And the use of sidewalls would mean it would have to be beneath a smooth, flat ceiling.

Reply
Jack G
11/21/2025 04:16:39 pm

20 ft is the limit and you must work out a series of soffits like the picture below
Meyer Fire pic from Feb 2024

Reply
Mark Fessenden link
11/24/2025 09:55:33 am

For this application, an anti-freeze loop with listed anti-freeze and a listed EC sidewall might be your best option.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT