MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Automatic Ball Drip Always Required for FDC?

6/6/2019

9 Comments

 
On recent inspections I've seen many installations where an automatic ball drip is not provided anywhere on the pipe connection between the fire department connection and the check valve that serves the fire department connection. Is there an exception I'm missing or isn't that automatic ball drip always required?

Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
9 Comments
Dan
6/6/2019 10:08:52 am

Refer to NFPA 13, A.8.17.2.6. It is required in areas subject to freezing. In areas not subject to freezing, where water would be trapped between the FDC check valve and the system, an auxiliary drain is needed.

Reply
Scott McCormick
6/6/2019 11:58:13 am

I am in a Local Enforcing Agency and was told by a sprinkler contractor that an Storz FDC doesn't need a ball-drip because its only needed on an FDC with a clapper, i do disagree because if the check valve doesn't hold the Storz FDC pipe could have water in it. My other comment is how contractor have put the ball-drip at the check valve when the check valve is not at the lowest point.

Reply
David Kendrick link
6/7/2019 09:08:56 am

Removing a Storz connection under pressure could be hazardous to the mechanic/fireperson.

Storz connections are not UL listed for fire protection use (or at least they weren't some time ago) for that reason.

While they are the trend and useful for the firefighters the design doesn't meet the original intent of the threaded FD connection.

Reply
Frank Herrick
6/7/2019 10:22:37 am

FDC ball drip is always required, regardless of Stortz or NH connection.

The purpose of the ball drip is to show the the FDC check valve isn't leaking, which will subject the FDC to being useless in the winter.

Question: Can ball drips be mounter in a horizontal position?

Yours truly, Capt. Frank J. Herrick

Reply
David Kendrick link
6/7/2019 10:49:03 am

As far as the question, personally I think it would depend on the ball drips design and manufacturers intent.
This not to avoid the question it is to address the particular installation and the devices intent.

For us the one's we use have to be in the horizontal position for the ball to move to the center of the housing and allow water to pass. Under pressure the ball is moved to cover the ball drip's outlet opening.

Reply
Jrob
6/7/2019 12:19:49 pm

I dont think I've ever seen a ball drip that you can install in the vertical position. I suppose if it was spring loaded it would work, but never seen one.

Reply
Pierre Lemieux
7/14/2020 06:23:13 pm

Most ball check models are required to be installed in the horizontal position (not all). You will usually see a 1/2" street elbow installed on the inlet side of the check making the ball check operate in a horizontal position.
A horizontal ball check will not work properly if installed in the vertical position.

Reply
Brian Cook
1/18/2021 07:36:30 am

“Yes” That is what makes them work properly, if they were installed in a Vertical position the ball would go to the bottom and block the flow

Reply
Jack G
6/12/2023 09:23:52 pm

A spring loaded ball drip can mount either vertical or horizontally. A normal plunger type, horizontally.
Another quandry is when nfpa required testing thru the siamese connection, i ve discovered when the check valve was in the basement and siamese at street level, the head pressure of water in that pipe was enough to close the ball so it wouldnt drain, without doing it manually, and not automatically.
It varies with manufacturer, but i use a 7 ft drop, as a cut off. Anyting more i add a drain valve along with the ball drip.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT