MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Drain Required with Each Pipe Drop Below Beam?

4/27/2021

17 Comments

 
In one of my jobs I have a fire sprinkler contractor who claims something that seemed strange to me. I have searched online but didn’t find the code section to show him.

He has laid out his Victaulic piping for two open space office under the beams and when I asked him why he didn't run them up high through the joists and instead only route the pipes underneath the beam where they have to, he responded that for each time that a pipe goes up and down, it requires a drain.

My question is in a wet sprinkler system in an office, do we need to provide drains for every time that a pipe is going few inches down and then back up? Since the entire system is wet and under pressure, are these drains necessary per any code? Whether we do require that or not, can anyone refer me to the pertaining code section?

​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
17 Comments
Jeremy Fowler
4/27/2021 08:14:01 am

Refer to 2016 NFPA 13 section 8.16.2.5 Auxiliary Drains. It pertains to how much water is trapped as to what the drain requirements are.

Reply
Bruce Seiler
4/27/2021 08:14:58 am

NFPA 13 (2019 Edition) Section 16.10.5.2 talks about auxiliary drains for Wet Pipe Systems. "Where the capacity of isolated trapped sections of pipe is 50 gal or more, the auxiliary drain shall consist of a valve not smaller than 1in. piped to an accessible location." If you are running a system high and dropping below beams, the likely hood of trapped sections containing more than 50 gallons (200 L)might be higher, although water would find its level and still drain where it could. If that trapped section of pipe is less than 5 gal ( 20 L), you merely need a plugged fitting or in the case of a Victaulic Grooved System, a grooved coupling. The reason for this requirement is to drain down the system properly when working on the system. If you don't have a properly drained/valved system, it will take a lot of 50 gallon drums to drain the system or a long hose running through the office building.

Reply
wnuk09
4/27/2021 08:19:31 am

I've come across this once before as well. In my opinion the contractor is correct in saying you need a drain where there's any location that water could become trapped. During some maintenance procedures, the entire wet pipe system needs to be drained for inspection. 2016 NFPA-13 8.16.2.5 addresses when an auxiliary drain is required.

Reply
Franck
4/27/2021 08:24:07 am

The purpose for properly draining all the system (even for wet system) is to limit possible corrosion issues (as well as to mimit water damages if you need to dismantle the pipes after drainage).

When you drain your entire system, all the pockets of water will be "fuel" for corrosion, and the longer you keep your system out of water, the more problems you will have.

Proper indication have been provided above on how to provide drain capacities depening on the trapped volume of water.

Reply
Glenn Berger
4/27/2021 08:26:27 am

When I am inspecting sprinkler system installations, one of the easiest punchlist items to spot is the omission of low point drains. No one has been able to prove that a drain is not required due to the small amount of water trapped.

It is recommended to put it in during the initial installation then trying to retrofit it during the inspection and test operations.

Reply
Franck
4/27/2021 08:29:41 am

Another explabation, for not going up and down, may also be related to the equivalent length for friction loss calcuation. If you go up and down and up again for each neam, this means 4 x 90° elbows, and dependning on the size of your pipe, this couild lead to high additionnaly friction losses in your system (as your feed main is used on its entire length with these up and down, not only at the most remote area).

Reply
Jesse
4/27/2021 08:31:10 am

Look at 2016 NFPA 13 Ch. 8.16.2.5.2 - this directs the size of the drain needed based upon the amount of trapped water.

Reply
James
4/27/2021 08:36:15 am

I see some architects/consultants request this kind of thing from time to time - just drop down below each beam and come back up.

It's easier said than done - not only is it a lot of fittings and a lot of friction loss, but there's far more labor cost to it as well. If pipe through the open-web joists is really desired, then the consultant should consider coordinating holes in the solid beams for a straight-run of branch lines. It would require significantly more coordination on the consultant's part, but it'd be cleaner and pipe would still be high. A good value-ad for being a consultant on the project.

Reply
Jon Sullivan
4/27/2021 09:34:21 am

Great advice. If you want to be on the structural engineer's good side, typically these penetrations should be in the middle 1/3 of the beam height and span.

It's a lot easier to have these fabricated in the steel shop rather than on site.

Reply
Casey Milhorn
4/27/2021 09:40:30 am

Agreed. We used to fight going "into the beams" but it's a great way to make sure you have the space all to yourself (mostly) and it's easier to get someone to move their stuff when you are in a designated spot and elevation. Might mean a few more couplings and little slower install, but I'll take the safe route over the unknown every time. But NEVER agree to torch the holes as a sprinkler sub. Way too much exposure in that AND sizes and locations must be approved by the structural engineer ahead of time. Also don't forget the seismic clearances required if on a seismic job. It could get very expensive using (2) flexible couplings at every hole.

Casey Milhorn
4/27/2021 08:53:55 am

Without looking it up, the old rule has been 5 gallons or less can be drained through a sprinkler in the pendent position or a plug or cap. Over 5 gallons to 50 gallons, a plugged valve of some sort is required. More than 50 gallons and a valve should be provided piped to an accessible location (typically outside, can wash, mop sink, near an outside door, etc). Those are my suggestions, not NFPAs. I don't think it goes into detail what an accessible location is. BUT, I would agree with the contractor that it is not a good practice to trap water without some very good reasons behind it. You are giving the building owner future headaches, corrosion issues, etc... that WILL translate into additional cost for the owner at some point down the road.

Reply
CJ Bonczyk
4/27/2021 09:18:03 am

Casey, completely agree with you and everyone else comments regarding this question. To answer your comment on what NFPA considers and accessible location... NFPA 13 2019 Handbook states accessible is the valve would be located approximately 7' A.F.F. to which a hose can be connected to discharge the water in an acceptable manner.

Reply
Jessica Lutz
4/27/2021 09:31:53 am

@CaseyMilhorn - THIS!!!!
Drainage consideration has come to the forefront in sprinkler design as of late. (The most annoying part of sprinkler systems...the necessary afterthought. I mean, for a long time the fitters would just take care of this in the field as they went along...not anymore.)
And I 100% agree with you on your guidelines.
Yep, and the "accessibility" definition angle...I've heard many interpretations.
I'd like to add, the larger capacity drains' termination points should be verified with all local building codes, as always.
Out in LA, they want them piped indirectly to sanitary hub drains.
In other surrounding counties, it's ok to pipe them to mopsinks, or floor sinks.

I could write a book...

Reply
Jon Sullivan
4/27/2021 01:39:13 pm

What plumbing code do they follow in LA? IPC allows any floor drain, mop sink, hub drain, or standpipe as an indirect waste receptor.

Jessica Lutz
4/27/2021 01:57:51 pm

@JonSullivan
They follow the CA Plbg Code, based on the UPC.
Sometimes, we're at the mercy of the inspectors also.
To avoid the argument altogether, I avoid trapping over 50 gal like the plague.

John Lane
4/27/2021 09:33:10 am

NFPA 13 (2016 Ed) Section 8.16.2.5.2.3 Covers everything Casey just said.

Reply
Jeff Garrison link
4/30/2021 09:18:05 am

We had CPVC in a residential highrise - 1.25" main where we
45'd maybe an inch under a few obstuctions (trapped water was about 8 oz.) and the AHJ made us put in a legal drain for each.
(cut-in and glued a tee w/ threaded plug outlet.)

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT