|
Working on a list of areas that should have or require drain connections for coordination with plumbing. Here's what I have:
(1) plumbing standpipe to accept main drain, where the main drain can't be routed to the outside, (2) floor drains in riser room as good practice; required if there's a pump or RPZ-type backflow, (3) plumbing standpipe to serve drainage from fire standpipes, where they can't be drained to the outside, and (4) standpipe or floor drain for remote inspector's tests & drains, where they can't be drained to the outside. What am I missing? Posted anonymously by a member for discussion. Discuss this | Subscribe
10 Comments
Frank J. Herrick
1/9/2019 10:43:30 am
Ensure the if the 2" main drain is piped to a floor drain, the drain piping is large enough to accept the full open discharge without causing flooding.
Reply
Brian Gerdwagen FPE
1/9/2019 02:06:37 pm
Depending on the water company, their requirements may not allow sprinkler water to go to sanitary sewer and may require storm sewer, or vice-versa.
Reply
Mike L
1/9/2019 07:48:03 pm
Inspector's test drain on sprinkler floor control valve assemblies.
Reply
Juan Davila
1/29/2020 10:41:31 am
Does anybody have a reliable and accurate formula to figure out the flow through the 3" gang drain for a high rise standpipe with PRVs..?. This to size the floor drain properly and to pass along to the plumber?.
Reply
Dean Melanson
1/23/2019 10:13:56 am
Don't forget - however it get plumbed - that the drain is also used for an annual main drain flow test under system pressure. The location that this drains into must be able to withstand the pressure and flow.
Reply
1/30/2019 06:45:41 pm
I have a wet sprinkler system fed by a combined standpipe/sprinkler riser by municipal water with a "brand new" fire pump in the basement. Question: Where should the main drain be installed? The municipal water enters the building and goes through the backflow preventer and then into the fire pump both being located in the fire pump room. Thereafter the riser goes to floor #1 and above. On the first floor there is a floor control valve with drain. I explained to property manager that a main drain is required in the fire pump room to test the adequacy of the water supply and drain the system. The installer agree with me but explained that is was not part of the drawing and he did not install one because he did not get paid for one. The property owner consulted with the engineer of record who said that the main drain is not in the fire code and that his plans got for the fire pump installation were approved by the Department of Building and he consulted with other more experienced engineers in his firm and was told that no main drain is required on the fire pump piping or in the pump room and if I want to drain the system or perform a main drain test I could do it from the first floor.
Reply
Joe Meyer
2/8/2019 07:02:38 am
Hi Vinny - good question.
Reply
Gary
7/21/2020 10:57:51 am
I have a question for fire hose connections in cabinets. Is the plumbing sub required to provide a floor drain next to the cabinet?
Reply
mark
3/8/2022 05:33:11 pm
Is there a NFPA code section stating specifically that a hub drain is required in lieu of a floor sink for fire sprinkler risers.
Reply
mariana
3/31/2023 04:29:15 pm
It does not say a hub is required necessarily, but where every it spills must be indirectly and the drain must be able to handle the capacity. Floor drains don't always meet the capacity requirements.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Sept '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
October 2026
PE PREP SERIES |
RSS Feed
