|
When using a draft curtain and closely spaced sprinklers at a floor opening for an exit access stair, what is the 18" depth for the draft curtain measured to?
The adjacent ceiling surface, or the deflector of the sprinkler? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Pete H
5/2/2025 07:03:29 am
The 18" depth of a draft curtain is measured from the ceiling down, like beam depth in construction.
Reply
Glenn Berger
5/2/2025 08:08:52 am
The 18" depth of a draft curtain is measured from the ceiling down, like beam depth in construction.
Reply
Pete H
5/2/2025 12:33:26 pm
Well, I like the cut of your jib.
Reply
Dan Wilder
5/2/2025 08:15:49 am
You can also look at NFPA 204 for additional requirements as that is where 13 pulled the info from. The application within 13 is limited to those couple of criteria (floor openings with closely spaced sprinklers AND draft curtains 9.3.5.2, separation of ESFR & standard response sprinklers 23.1.2, and sometimes where not allowed as in general use within ESFR systems - 20.9.5.3, adjacent hazards/design methods 19.1.2 & 20.13 for example)
Reply
Jesse
5/2/2025 08:36:45 am
From the ceiling.
Reply
Todd E Wyatt
5/5/2025 07:25:17 am
Other requirements for DRAFT CURTAINS per the referenced standard (NFPA 13-2022) by the scoping code (IBC-2024) :
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Oct '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
November 2026
PE PREP SERIES |
RSS Feed
