I have a 9-story residential building with 3 levels of parking. The building requires a fire pump. The AHJ limits us to a design pressure of 60 psi regardless of the available water pressure.
In my case, the available pressure is 85 psi static, and I have a 115 psi fire pump with a 134 psi shutoff pressure. Therefore, I need to reduce the pressure to ensure that the system does not exceed 175 psi. I am planning a double pressure reduction, with the first reducing valve set at 162 psi and the second reducing valve set at 165 psi, with the second valve essentially acting as friction loss only. Assuming a 5 psi pressure increase per floor, would it be acceptable to supply two basement levels below the pressure-reducing valves and reach 172 psi at those levels? I have already noticed that PRVs can have up to 10 psi above their set point under static conditions, which would make the pressure exceed the maximum limit of 175 psi. To eliminate this overshoot, I plan to install a 1-inch pressure relief valve set at 165 psi to ensure that the system pressure never exceeds 175 psi. This solution seems ideal, except in the event that the pressure-reducing valve is unable to stabilize the downstream pressure below 165 psi. In that case, both the pressure-reducing valve and the relief valve would remain slightly open, allowing a continuous flow of water. This could cause the jockey pump to start repeatedly in an attempt to maintain system pressure, potentially resulting in premature wear of the pump. Do you have any advice to help me in my design? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Brett
10/14/2026 10:22:32 am
I recommend reviewing the manufacturer cutsheets for the pressure regulating valves closely and contacting them if you still have questions. All the master pressure regulating valves I've looked at recently require minimum 10-20 psi drop across the valve. Also consider the minimum flow rate through the valves and whether it can handle the low flow of one sprinkler flowing water.
Reply
10/14/2026 10:43:43 am
First, you have to find out why the AHJ has a 60 psi design pressure. One the surface, this seems completely illogical.
Reply
Dan Wilder
10/14/2026 02:11:18 pm
I've got one that only allow 45PSI....maximum static.
Reply
Dan Wilder
10/14/2026 02:36:02 pm
Any of the larger PRV (pilot operated) will also require a low flow bypass and the UL listing limits them to 165PSI along with the minimum loss across the valve once the residual pressure lowers the pressure enough for that to become a factor.
Reply
Bryan L
10/15/2026 09:26:46 am
Thanks for your answer Dan.
Reply
Jack G
10/14/2026 07:45:38 pm
The 60# is curious.
Reply
Jack G
10/14/2026 07:51:41 pm
I also like the idea above of splitting and running a separate sprinkler only riser to the parking floors that would operate unde Streep pressure. Appropriate FDC connection arrangement so that 1 FDC Will supply both.
Reply
Nimal Tissa Wijetunga
10/15/2026 05:35:57 am
Considering the system requirement,friction losses and static loss, the best practise is to have two set of Fire pumps and water tanks for basement floor and the higher floors separately in line with fire engineering where maximum pressure to be maintained at or below 175 psi.
Reply