Does NFPA 30, 31, 37 Apply to Diesel Generators?

12/6/2024

6 Comments

 
What NFPA Standard(s) apply for two diesel generator tanks?

Two diesel generators (not emergency or standby), outside (but
have enclosures) with each diesel tank stored underneath, the tank is rectangular in shape and has ~5,000 gallons of diesel fuel.

Looking at the following code path; IMC Chapter 13 for fuel oil piping and storage and IFC Chapter 6--> 605.4 Fuel Oil Storage Systems --> storage above ground in quantities exceeding 660 gallons --> NFPA 31; OR IMC Chapter 9 engine and gas turbine-powered equipment and appliances.

Is this approach correct?

In reviewing both NFPA 37 and NFPA 31, both seem to be applicable
; however, when it comes to "outside aboveground tanks" of this capacity, they both reference NFPA 30 (Section 6.3.3 for NFPA 37 and 7.9.3 for NFPA 31).

So here's the main question - is NFPA 30 applicable here?

I base this on a few things:

1. NFPA 30 Scope section 1.1.2 item 9 - it says it is NOT applicable to "liquids in fuel tanks of... stationary engines" ; and
2. All the boundary and tank to tank separation requirements throughout chapter 22 are based on the diameter of the tank.

This leads me to believe this standard was not written for the type of tanks I have, but instead typical giant circular storage tanks.?

Any insight is greatly appreciated.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Glenn Berger
12/6/2024 08:15:46 am

It appears that your project is using a belly tank that is basically integral with the diesel generator assembly.

If correct, then NFPA 30 is not typically applied to this situation.

Reply
Jimmy
12/6/2024 08:30:11 am

The difference is the use.

>Storage tanks are used for dispensing.
>The generator tank is dedicated and mounted to the unit.

Reply
Jesse
12/6/2024 09:07:08 am

NFPA 30 wouldn't apply to this. You're not dispensing from the tank to another process element. This is the tan for thestationary equipment

Reply
Brett
12/6/2024 09:51:04 am

Does NFPA 30 apply when the tanks are located away from the generator (either remotely outside or in the same room) and fuel is pumped to the generator?

Reply
Ryan L. Hinson
12/6/2024 11:13:58 am

It is my opinion that NFPA 30 DOES apply as directly referenced from a more specialized 'occupancy' standard such as NFPA 31 or 37...if those standards are adopted in the jurisdiction. As an example, see NFPA 11 (2024) Section 6.5 where 'occupancy standards' might take precedence. See also NFPA 37 (2024) Section 1.5 - Equivalency and Section 2.1 of both NFPA 31 and 37 which states:

"The documents or portions thereof listed in this chapter are referenced within this standard and shall be considered part of the requirements of this document."

Reply
Douglas True link
12/16/2024 11:48:23 am

Although NFPA 30, subsection 1.1.2(10) states that nfpa 30 is not applicable to "liquids in the fuel tanks of motor vehicles, aircraft, boats, or portable or stationary tanks." Both NFPA 1 and NFPA 37 state otherwise:

The storage, use and handling of flammable and combustible liquids including waste liquids as herein defined and classified shall comply with the requirements of 1:66, NFPA 30 and 1:60.1 through 1:60.4. [1:66.1.1* (NFPA1, Subsection 66.1.1)]

Where the provisions of 1:66 or NFPA 30 conflict with the requirements of 1:60 the provisions of 1:66 and NFPA 30 shall apply. [1:66.1.2 FL]

Fuel tanks located outside, either aboveground or underground, or located underneath a structure shall comply with the applicable provisions of NFPA 30. [37:6.3.3]

Diesel fuel is a Class II combustible liquid - in this instance the MAQ is exceeded exceeded with 10,000 gallons stored in a single control area. [30:T.9.6.1 (T = table)]

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT