NFPA 14 requires PRV redundancy when more than two hose connections are supplied downstream of a PRV.
Does NFPA 13 have a similar requirement for sprinkler systems, or can multiple sprinkler systems be controlled by a single PRV? We are proposing to feed a riser manifold controlling (6) sprinkler systems to be supplied by a single ORV without a redundant loop. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Dan Wilder
4/3/2026 07:57:02 am
Not specifically called out in 16.9.7 (13-25) for Pressure-Reducing Valves.
Reply
Jesse
4/3/2026 08:25:12 am
I was wondering if I was understanding the issue as intended because I agree with Dan's point. I think this could impair all systems.
Reply
Jose Figueroa
4/3/2026 11:13:00 am
Yes, this makes sense in principle. However, I need more details: if you share the specific NFPA edition you’re working with, the building height or occupancy type, or whether this system is a combined standpipe and sprinkler setup, I can help narrow it down further. In most standalone sprinkler applications, your single-PRV manifold approach aligns with NFPA 13.
Reply
OP
4/3/2026 04:07:02 pm
2022-NFPA 13, CBC 2022, Non-FM Global. I have a horizontal riser manifold, feeding (6) sprinkler risers (on the same floor), in a high-rise (4) story building. The proposal is to install a single PRV prior to the first riser instead of installing (6) individual PRV valves, which would be a single PRV for each system.
Reply
OP
4/3/2026 04:12:12 pm
Standpipe system is separate of the horizontal riser manifold and will not be controlled in this instance.
Jose Figueroa
4/3/2026 05:25:16 pm
@OP
Jack G
4/3/2026 04:51:54 pm
The PRV and riser manifold would be sized for the 6 sprinkler risers on that floor.
Reply
Jose R Figueroa
4/6/2026 01:28:49 pm
Reply
Rocket
4/16/2026 12:47:53 pm
Based on practical experience, I advocate for the use of dual PRVs as a contingency measure, without referencing specific Standard sections.
Reply