Does IBC or NFPA 13 Precede When in Conflict?

9/16/2024

10 Comments

 
We have a mass timber building. It's Type III-A construction with an NFPA 13 system.

The building has a large exterior roof canopy (more than 4-ft wide) primarily used as a pedestrian walkway and building entrance.

For these types of roof projections, overhangs, canopies, etc., IBC Section 705.2.3 allows the following options:
  • Noncombustible construction
  • Combustible construction with a 1-hr FRR
  • Heavy timber construction (meeting minimum sizes in accordance with 2304.11)
  • FRTW
  • Or, in accordance with Section 705.2.3.1 for balconies – which basically gives you the same options as those listed above, with the additional option of extending sprinkler protection to those areas.

However, in the NFPA 13 standard (Section 9.2.3), it seems to only allow the following options for omitting sprinklers from these locations:
  • Noncombustible construction
  • Limited combustibility construction
  • FRTW – which is not available for most mass timber products, including CLT
  • If combustible construction is used, it has to be covered in a finish material that meets one of the options listed above (with additional limitations on concealed spaces).

These two codes seem to be at odds with each other and it’s not clear to me which one governs. The IBC clearly allows the use of a 1-hr rating or heavy timber, both of which would allow this particular project to omit sprinklers from the exterior roof canopy. However, NFPA 13 seems to require the use of sprinklers at these locations.

​Does the IBC allowance overrule NFPA 13 here? Or does NFPA 13's requirements overrule the IBC?

What's the code basis that would support priority of one or the other?

Appreciate any insight or how you've seen these situations handled on other projects.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Peter Howard
9/16/2024 06:48:42 am

I'm sorry, I don't know if I see the conflict.

IBC is telling you code acceptable types of balconies/overhangs you can install.

NFPA 13 is telling you when the projection can omit sprinkler protection.

If you built it using the IBC requirements and it does not fall into the NFPA 13 allowances, you need to protect it with sprinklers.

If you built it where it works with both, you can omit sprinklers.

And if you didn't build it using the IBC requirements, you have bigger problems.

Reply
Anthony
9/16/2024 07:55:07 am

I agree with Pete here. IBC tell you how to build it. NFPA 13 tells you how to protect the building with sprinklers.

To answer the broader question of which code takes precedent, a state adopted version of ICC model standard or NFPA 13, its always the adopted code.

Reply
Joe
9/16/2024 08:08:45 am

Hierarchy
The Administrative law adopted by the jurisdiction.
The adopted codes
The referenced standards
Code always trumps the standard

Reply
Sean H
9/16/2024 08:08:57 am

The IBC in this case wins (and calls itself the winner).

IBC 2018 example

Chapter 1 Scope and Administration > Section 102 Applicability >
102.4.1 Referenced Codes and Standards >
102.4.1 Conflicts: Where conflicts occur between provisions of this code and referenced codes and standards, the provisions of THIS code shall apply.

There's more good stuff in that front section. I can't speak to the specifics of the NFPA 13 and IBC conflicts you note above, but I found this section in the IBC interesting when I became aware of it a few years ago.

Reply
Justin Rosales
9/16/2024 08:47:28 am

Actually IBC does direct the user to follow NFPA 13 for constructing a sprinkler system so referring to Ch 1 would not be applicable.

§903.3.1.1 - "Where the provisions of this code require that a building or portion thereof be equipped throughout with an automatic sprinkler system in accordance with this section, sprinklers shall be installed throughout in accordance with NFPA 13 except as provided in Sections 903.3.1.1.1 and 903.3.1.1.2."


In the except locations they list IBC clarifies that just because something is fire resistance it is not a good enough reason to omit sprinklers. Hypothetically, if there was a conflict between IBC and NFPA the code official is going to go with the more stringent requirement that provides a higher level of safety for the occupants. The only way I could see the AHJ approving the omitting of the sprinkler is if this balcony exceeds 50 ft in height and even then they might ask for a model to prove that the sprinklers wont activate.

Reply
Zackery Geddies
9/16/2024 08:10:05 am

Usually the more stringent code applies when there is a conflict.

Reply
Glenn Berger
9/16/2024 08:10:59 am

Concur with previous responses. But in general most stringent rules would be the starting point.

Reply
Todd E Wyatt
9/16/2024 08:13:10 am

The scoping Code (e.g. IBC-2018) determine WHERE an automatic sprinkler system (ASPS) is to be installed.

The scoping Code includes “Exempt Locations” where an ASPS is not required :

Section 903 Automatic Sprinkler Systems
903.3 Installation Requirements
Automatic sprinkler systems shall be designed and installed in accordance with Sections 903.3.1 through 903.3.8.
903.3.1 Standards
903.3.1.1 NFPA 13 Sprinkler Systems
Where the provisions of this code require that a building or portion thereof be equipped throughout with an automatic sprinkler system in accordance with this section, sprinklers shall be installed throughout in accordance with NFPA 13 except as provided in Sections 903.3.1.1.1 and 903.3.1.1.2.
903.3.1.1.1 Exempt Locations
Automatic sprinklers shall not be required in the following rooms or areas where such rooms or areas are protected with an approved automatic fire detection system in accordance with Section 907.2 that will respond to visible or invisible particles of combustion. Sprinklers shall not be omitted from a room merely because it is damp, of fire-resistance-rated construction or contains electrical equipment.
1. A room where the application of water, or flame and water, constitutes a serious life or fire hazard.
2. A room or space where sprinklers are considered undesirable because of the nature of the contents, where approved by the fire code official.
3. Generator and transformer rooms separated from the remainder of the building by walls and floor/ceiling or roof/ceiling assemblies having a fire-resistance rating of not less than 2 hours.
4. Rooms or areas that are of noncombustible construction with wholly noncombustible contents.
5. Fire service access elevator machine rooms and machinery spaces.
6. Machine rooms, machinery spaces, control rooms and control spaces associated with occupant evacuation elevators designed in accordance with Section 3008.
903.3.1.1.2 Bathrooms

Otherwise, the ASPS standard referenced (e.g. NFPA 13-2019) “shall be installed throughout in accordance with NFPA 13.”

Reply
Ken Thackery
9/16/2024 10:13:09 am

When the ambiguity arises 1. clarify with an RFI ASAP and put it back into the Arch/design teams court for an answer. 2. Consult an FPE. 3. Also depending on schedule if you can submit to the AHJ also ASAP and wait for their comments, or call them. Is it 5 heads or 50? If its 5 just add them, its not worth fighting over or having to add them after the fact.

Reply
Justin Phillip Milne
9/18/2024 04:52:20 am

There is something that the others do not appear to clearly address here.

The International Building Code (IBC), is a code, meaning it has more legal authority. The NFPA 13 Standard, is a standard, meaning that it is only used when directed by a code. You are legally bound to follow NFPA 13, because the International Building Code tells you to, as mandated by law.

https://www.nist.gov/buildings-construction/understanding-building-codes

Now, apart from the code issue, Mass Timber is a completely separate concern. The IBC will be more developed on Mass Timber issues than NFPA 13. With that said, if the jurisdiction is open to it, you may have the opportunity for an engineering judgement here, if the code authority will allow it.

If you have more questions on that, feel free to reach out.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT