|
NFPA 14 states that "hydraulically designed standpipe systems shall be designed to provide the waterflow rate required by Section 7.10 at a minimum residual pressure of 100 psi at the hydraulically most remote 2½" hose connection and 65 psi at the outlet of the hydraulically most remote 1½" hose connection" (Section 7.8.1, 2019 edition).
So does this mean if you have a single 2½" hose valve on your project, you need 100 psi residual at that valve? This seems pretty cut and dry, but I've been thinking about this, and off the top of my head, I can list at least 5 projects that had 2½" hose valves and less than 100 psi of static pressure on the ground floor, let alone 100 psi residual on the 4th floor. Not only projects that I have personally witnessed get signed off, but also buildings I have found myself walking through that have had gauges on the hose valves, and those gauges more often than not (in my area at least) read a pressure less than 100 psi static. Are these just all designed wrong? Or am I missing something? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Brett
3/31/2025 06:49:08 am
How tall were those buildings? It sounds like those projects may have had manual standpipes which means the fire department's pump would be the one boosting the pressure of the system.
Reply
danefre
3/31/2025 07:29:28 am
Read about automatic vs manual standpipes.
Reply
Taylor Schumacher
3/31/2025 08:28:28 am
Sounds like you are looking at manual wet standpipes.
Reply
Jesse
3/31/2025 08:33:47 am
I think you may be looking at manual a wet-standpipe system. While this may be interconnected to the AS system, a fire department apparatus is required to supply the system to operating pressure. As such, the static pressure on the system isn't of much relevance.
Reply
Glenn Berger
3/31/2025 08:51:21 am
The design needs to account for 100 psi at the most remote outlet. This can be achieve via the pump on a fire truck as is typically for a manual-wet standpipe system. Placard needs to be provided for the responding fire department to achieve the required pressure.
Reply
Jack G
3/31/2025 08:52:42 am
It s probably a manual wet standpipe system where the fire department supplies the pressure and flow to the standpipe system.
Reply
Dan Wilder
3/31/2025 08:56:56 am
There are also provisions within NFPA 13, 16.15.2.1-19 Ed. for adding 2½" hose valves (not typically in buildings over 30' as that is the trigger for standpipes).
Reply
Matthew Mueller
4/1/2025 09:55:34 am
Regarding the 100 psi minimum, it's important to remember the historical context. Prior to the early 2000s, BOCA standards, a predecessor to the IBC, (as well as NFPA 14 if I am correct) specified a minimum of 65 psi. This was based on the smooth bore nozzles used by the fire service until the 80s/90s.
Reply
Dave L.
4/7/2025 10:15:20 am
Note that for hose stations that are NOT part of an NFPA 14 standpipe system, requirements may vary.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Oct '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
November 2026
PE PREP SERIES |
RSS Feed
