Questions about extended coverage sprinklers and grey areas: Say you have a mix of Reliable G4 XLO extended coverage sprinklers and Tyco ELOC's in an existing property. They are protecting a variety of 16' x 16' applications as well as 20' x 20'.
The Tyco sprinkler, per the cutsheet, becomes standard response at 20' x 20', but the G4XLO EC only becomes standard response in Ordinary Hazard at 212 degrees. The space is all either light hazard or all the heads applied are 155-165 degrees. Do you have to look for and replace every Tyco head operating at 20' x 20' because it's a contradictory response type, and can you leave the ones that are 18' x 18' or less? You have an extended-coverage sprinkler in a small room to protect the entire room. Due to the placement of the lights, you can only be 10'-0" off the wall in one direction, but are within 7'-0" of all other three walls. The room is 17 x 14 feet and light hazard. The room is 238 square feet. This is less than the 256' max of a 16' x 16' application, but since you're 10' off a wall, is this equivalent to a 20' x 20' application when you're figuring out the appropriate pressure for the head in your calculation? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Dan Wilder
10/7/2026 08:42:16 am
So, in 13-2019 edition and later, based on EOD questions:
Reply
Brett
10/7/2026 09:05:45 am
I answered the questions below based on NFPA 13 criteria and the assumption that you're already doing sprinkler system alterations in the area. If these questions are coming as a result of an NFPA 25 inspection in an existing building then I don't think NFPA 25 would require anything to be adjusted.
Reply
Jack G
10/7/2026 04:25:52 pm
I agree with Brett above. And reviewing the material data sheets the reliable qr sprinkler has an RTI of less than 50 ( the standard for qr) also the tyco head spaced at 20 x 20 has an RTI over 80 which makes it Standard response.
Reply
Jack G
10/7/2026 04:47:01 pm
Reviewing the tyco cut sheet, they are not listed for ordinary hazard an is another reason to replace with the Reliable sprinklers .,