Does a Water Storage Tank Need to be UL Listed?

3/31/2026

9 Comments

 
Is a water storage tank for an NFPA 13 system required to be UL listed, or does it need to simply be NFPA 22 compliant?

I was always taught that a tank had to be at least UL Listed for fire protection, but I have a supplier telling me otherwise, and the price he offers is less than half that of a UL/FM tank.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Pete H
3/31/2026 06:44:42 am

Doesn't fully answer the question but this page does have a tangentially interesting write up on the difference between NFPA 22 compliant and NFPA 22 Equivalent:

https://waterstoragetanksinc.com/category/nfpa-22/

Reply
Dan Wilder
3/31/2026 08:11:09 am

Since I was in this section yesterday...

13 requires the water supply from a tank to be installed in accordance with NFPA 22 (Chapter 5 - Water Supplies)

NFPA 22 Chapter 4 provides General Information, none of which states anything listed or approved is required, other than for the AHJ. I also searched for the words "listed" and " approved" and they are rarely mentioned beyond specific parts or assemblies (ladder safety, roof construction by the AHJ,

There are requirements for approval from the AHJ, so that may be a limiting factor upon submittal. Materials must be listed and/or approved for their use in construction of the tank, but I don't see anything on the overall. I also checked out some bids we have received and very few showed anything more than verbiage about "meets industry standards of NFPA 20, 22, 1142" or "manufactured in compliance with NFPA requirements"...for fiberglass, concrete and steel construction.

Reply
John Callahan link
3/31/2026 08:15:17 am

The welded or bolted steel tank shall conform to the requirements of AWWA D102-17 for welded tank, AWWA D103-19 for bolted tanks, FM Global Data Sheet 3-02 and NFPA 22 - Standards for Water Tanks for Private Fire Protection, Current Edition.

Reply
Moderator
3/31/2026 08:20:16 am

John - appreciate the input. On what basis do these standards apply? Generally speaking, code and standard references help substantiate requirements for readers going forward. Thanks!

Reply
Glenn Berger
3/31/2026 08:32:47 am

NFPA 22 - 2023 edition has the following statements that are applicable to this topic:

4.11 - Materials produced and tested in accordance with the requirements of a recognized national standard and within the mechanical (strength), metallurgical, and chemical limitations of one of the material grades specified in this document shall be permitted.

5.2.1 - All tank foundations, materials, accessories, fabrication, construction, and welding shall be in accordance with AWWA D100 or AWWA D107. (welded Tanks)

6.2.1 - All design materials, fabrication, and installation shall be in accordance with AWWA D103. (Bolted Tanks)

I am sure that other references can be found. But a direct relationship to UL listed or other nationally recognized testing labs is not present in this standard for the entire water storage tank assembly.

Side note: Be careful when you see a "label" saying that a tank is "NFPA approved." You were correct is asking about NFPA 22 compliant.



Reply
Ken Thackery
3/31/2026 10:06:29 am

The short answer is no. The tank is under Div 33, not Div 21. We have done 2 in the last 2 years one Xerxes, one Fiberglass Tank Solutions in MO- made tanks for Xerxes, 1/2 the cost- It's just a water storage tank buried in the ground. Think if you had a concrete tank under a high rise for a vert turbine or horizontal pump, obviously not UL approved, it's essentially a giant swimming pool. Sometimes we tend to overcode everything when we need to keep it simple.

Reply
Josh
3/31/2026 11:03:48 am

I have specs in div. 21 for ground-suction tanks. It's fire-only. 24 41 23. I think it depends on the type of tank. I think the underground fiberglass go in division 33 where others like ground-suction steel, bolted are 21.

Reply
Jose R Figueroa
3/31/2026 10:31:27 pm

There are “FM Approved” fire tanks, and they are widely used to ensure reliable water supply for fire protection systems, meeting strict FM Approval standards (Class 4020/4820) for structural integrity, earthquake resistance, and wind resistance. These tanks comply with NFPA 22 standards, and are manufactured by companies like CST Industries, Center Enamel, Fire Tank Pros, Balmoral Tanks, and others. These tanks should probably carry the UL listed seal.

Reply
Jose R Figueroa
4/1/2026 10:19:02 am

I forgot to mention: The AHJ and insurance companies might require water tanks to be FM Approved or UL Listed. For example, if this is an FM client, please contact FM Engineering for more information before investing in the fire water tank.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT