MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Does a Hydrant Fed From Building Meet Code?

3/4/2025

14 Comments

 
My jurisdiction (I am the AHJ) has had several buildings built with private hydrants supplying the sprinkler system where the main comes into the building, through the RPZ, feeds the sprinkler system/standpipes, and leaves the building and feeds the hydrant(s).
Picture
This has always seemed counterintuitive to me, at best. I feel we are "robbing Peter to pay Paul" and have wondered if this arrangement will adequately supply the sprinkler system when we (FD) pull water from the hydrant and pump it back into the FDC.

Per our state law, private hydrants have to be "protected" with a backflow.

Is this configuration code compliant, and if not, what is a solution?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments
Pete H
3/4/2025 06:34:32 am

It really should be fed off a bypass line instead of going through the double check for a cleaner install imo.... but as long as the hydrant can calculate the required water and meets code in every other way, a private hydrant can be fed from main that goes through a building.

And it's not exactly like it's terrible it goes through the double check, as there are private hydrants in some master-metered communities.

But as long as the hydrant has the required flow and pressure and the double check and internal piping (different c factor if applicable, elbows and tees, etc.) are included in the calculations, this isn't against code as far as I know. Warning/take with a grain of salt: I'm not specifically checking the code as much as I'm thinking of existing buildings where I've seen this before when saying this response.

Reply
Dan Wilder
3/4/2025 06:59:50 am

While not common, if calc's prove it works I see no code-based opposition. Review of the max flow through the backflow to confirm sprinkler and hydrant demand does not exceed the max flow (plan on one or several increases in sizing to accommodate max flow or valves in parallel).

In this setup though, the FDC is useless as it will just feed back out to hydrant in a loop (the red arrows illustrate this well). Using Pete's idea of a bypass prior to the backflow would solve the issue or there would need to be individual connections to systems, all with their own checks, to avoid recirculation. Alternate arrangement could have the feed to the hydrant come off right after the backflow, then through a check valve, then to the rest of the system and FDC (basically switch the hydrant & FDC lines and add a check valve. If the flow switch is needed for the hydrants, that would also need to be pulled back.

Reply
Mike Morey
3/4/2025 08:14:37 am

In the cases where we've done this we've ensured that there is still a city side hydrant near the FDC and only used it for hydrants beyond the pump/riser room. Large building loops are built this way all the time at spec/shell/warehouse buildings. Biggest issues are ensuring you can provide the required site fire flow or portion there of the AHJ wants from the hydrant(s) and accounting for the hydrants connection point as your hose stream demand point in the sprinkler calc.

Reply
Joe
3/4/2025 08:38:09 am

Not normal but you would have the same issue if after the back flow device you install underground piping with hydrants spaced per you code and then somewhere you have a leadin going into the build for the sprinkler systems

As other said check the cut sheet for the backflow, and make sure you have done a good flow test on the public water line. I always try to flow two 2 1/2 or one 4 AM inch outlet to stress the systems.

Reply
Casey Milhorn
3/4/2025 08:42:27 am

What Mike M said... typically I suggest a public hydrant as the hydrant used for the pumper truck. Also what Pete said, a bypass line WITHOUT a control valve would be best in my opinion. That way you still have hydrant flow if the backflow is out of commission and valves are closed off. It appears as if you might have a decent size building and I would be concerned that you would be able to meet your fire flow demand through that backflow, not to mention the amount of pressure loss across a RPZ will be considerable. With a 6" Wilkins 375, you are maxing out it's listing at 1,500 gpm. I would imagine your fire flow demand is at least 1,500 gpm.

Reply
Glenn Berger
3/4/2025 08:55:22 am

As long as the system supply can support the maximum expected flow through sprinklers and the exterior hose connections that the layout seems acceptable.

Many thoughtful responses have been provided to this question.

Reply
Anthony
3/4/2025 09:09:01 am

this appears to be legal with an RPDA/RPZ however, the calc's will get more difficult as the hose allowance will have to be take out after the water has passed by the supply for the sprinkler system. I think this may cause over sizing on the sprinkler system you'll want the hydrants that to tee off prior to the system supply.

Reply
DJT
3/4/2025 10:19:03 am

The hydrant supply needs to be separated from the FDC. As it's shown the FD pumper will circulate water from the hydrant and pump it back through the FDC as the arrows indicate. This risks checking the incoming water supply back until the sprinkler discharge drops the system pressure, rendering the FDC/pumper useless. The two solutions are either tee off to hydrant from upstream of the FDC tee while adding another check valve between the two connections, or move the FDC to tie into each riser above their check valves. Some problems don't have code justification.

Reply
Jack G
3/4/2025 10:56:00 am

First of all I would add an fdc check to each of the sprinkler systems and a check at the end of the manifold before the tee going to the hydrants. Then I d tie the checks into one fdc.
This way you avoid a ( loop ) between the hydrants and the fdc.
Language in 24 leads you to run 6 inch to 2 hydrants and 2 sprinkler systems but 8 inch to more systems.
I ve also run supplies to “ wall hydrants “ on the opposite walls of the building with wall post indicator valve to open and connect to the wall hydrant and avoid lots of underground piping if permitted by the AHJ.

Reply
Jack G
3/4/2025 11:02:28 am

And you could add an fdc to the far side of the building ( bulk and check) to use in combination with the wall hydrants and common fdc.
I also don’t like the rpz loss on the systems no matter which configuration, but if required, what can you do ?

Reply
Jack G
3/4/2025 11:06:10 am

I would also use OS&Y Valves on each side of the rpz with the appropriate tamper switch instead of the gate valves shown.

Reply
Jack G
3/4/2025 11:13:54 am

Of course the fdc shown would not be tied in where shown but after the 5 checks added ( tied into 1 fdc , and or another on far side of the building) and I d make the fdc a storz and or 6 inch fdc, for the hydrants .

Reply
Ed
3/4/2025 12:22:12 pm

DJT is correct. The current arrangement will not work. The fire hydrant supply has to be before the tee for the FDC with a check valve in between. Otherwise, the system will not pressurize appropriately since you are recirculating the flow.

Reply
Mark Harris
3/5/2025 03:18:54 pm

Great comments. Made me think about a distribution center that could have a booster pump or pump and tank fed from city supply with FDC on the pump house and as noted the pumper truck supply for FDC would need to be a supply hydrant before the pump house. Then could have private underground loop with private hydrants and supply into building for sprinkler risers.

Don't see much anymore but used to occasionally see wall hydrant connection on back of building with a wall PIV to control water supply. Sometimes to have fire water source for rail siding, idle exterior pallet storage or maybe truck trailers. But those days were not million square foot buildings with dock doors all the way down two sides so private underground fire loop with hydrants is more common today.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT