Does 25% Opening Limit Affect Door in Fire Wall?

9/3/2026

7 Comments

 
I'm working on a church youth building in a rural area and trying not to sprinkler due to cost. Occupant load of each wing is under 300. Wings to be separated with a double fire wall between the lobby and the east wing.

NFPA 221 (2018) Section 6.10.1 requires the length of openings not to exceed 25% of the fire wall length.

Does that apply in this scenario? See image below for openings within the fire wall.

​(Note: There are other emergency exits for the west wing not shown in the image for use in case of fire.) Thank you for your help.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
7 Comments
Pete H
9/3/2026 06:18:14 am

I'd check NFPA 80 to see if there's some exemption, but everything I'm seeing includes fire doors within "opening protectives"

Reply
Glenn Berger
9/3/2026 08:25:06 am

I need to see a complete code analysis -

Are you trying to indicate a double fire wall from the right side Assembly Space?

Do you really have a fire wall or just a (double) fire barrier?

In most jurisdictions, you can not use roll up doors in a means of egress.

Reply
Todd Wyatt
9/3/2026 08:36:58 am

Review the scoping Code (e.g. IBC-2024 and IEBC-2024) to see if the Addition is exempt from automatic sprinkler protection (ASPS) protection :

IBC-2024
Chapter 9 Fire Protection and Life Safety Systems
Section 903 Automatic Sprinkler Systems
903.2 Where Required
903.2.1 Group A
An automatic sprinkler system shall be provided throughout buildings and portions thereof used as Group A occupancies as provided in this section.
903.2.1.3 Group A-3
An automatic sprinkler system shall be provided throughout stories containing Group A-3 occupancies and throughout all stories from the Group A-3 occupancy to and including the levels of exit discharge serving that occupancy where ONE of the following conditions exists:
1. The FIRE AREA exceeds 12,000 square feet (1115 m2).
2. The FIRE AREA has an occupant load of 300 or more.
3. The FIRE AREA is located on a floor other than a level of exit discharge serving such occupancies.

A Fire Barrier (FB) vs a Fire Wall (FW) is permitted to separate the same building (Existing + Addition) into Fire Areas (FA) that may exempt them from being protected by an ASPS.

IBC-2024
Chapter 7 Fire and Smoke Protection Features
707.3.10 Fire Areas
The FIRE BARRIERS, fire walls, horizontal assemblies or combinations thereof separating a single occupancy into different fire areas shall have a fire-resistance rating of not less than that indicated in Table 707.3.10. The FIRE BARRIERS, fire walls, horizontal assemblies or combinations thereof separating fire areas of mixed occupancies shall have a fire-resistance rating of not less than the highest value indicated in Table 707.3.10 for the occupancies under consideration.

If a Fire Wall was used for other reasons (Allowables ... Building Area, Building Height, Number of Stories), the maximum opening in a FW in a non-sprinklered building is 156 square feet and the aggregate width of openings at any floor level shall not exceed 25 percent of the length of the wall :

IBC-2024
Chapter 7 Fire and Smoke Protection Features
Section 706 Fire Walls
706.8 Openings
Each opening through a fire wall shall be protected in accordance with Section 716 and shall not exceed 156 square feet (15 m2). The aggregate width of openings at any floor level shall not exceed 25 percent of the length of the wall.
Exceptions:
1. Openings are not permitted in party walls constructed in accordance with Section 706.1.1.
2. Openings shall not be limited to 156 square feet (15 m2) where both buildings are equipped throughout with an automatic sprinkler system installed in accordance with Section 903.3.1.1.

Reply
Louie Lincoln
9/3/2026 08:45:00 am

I don't see why anyone would not want to utilize sprinklers. They work 24hours a day seven days a week. You don't get that with any other protection. I would use sprinklers first then look for any other protection.

Reply
Conrad
9/3/2026 01:27:15 pm

A few points to consider:

To count as separate buildings, the east wing must have an independent exit leading directly outside.

A 1-hour barrier is not enough. Separating buildings requires a structurally independent fire wall (typically 2 to 4 hours).

The 299 figure is a threshold workaround and will draw the plan examiner's scrutiny.

Reply
Jack G
9/3/2026 04:05:41 pm

I d like to see a code analysis and the entire 2 wings with fire walls windows and exits,,.....but how i see this per 1006.2.1,2.2thru 2.6 :
For 300 occupancy 2 exits are required, exit door 60 inches ( non sprinklers, 45 inches sprinklered. The wings exit thru the lobby, but there is only 1 exit door.
Now if you look at the 2 wings emptying into the lobby ,the requirement is 3 exits for 501 to 1000 occupants.
Need at least 2 exis more on each wing plus the common lobby one for a total of 3 exits.

Reply
Donnie Brewer
9/3/2026 05:16:20 pm

Must have a minimum number of 3 approved exits. The occupant load exceeds 300, so sprinklers are required. Have you done the cost analysis to determine the difference ? If you build non separated use sprinkled throughout theres is no need to separate the building using expensive fire rated assemblies, doors, dampers, etc. that are often not maintained properly.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT