My area's adopted building code references NFPA 13, the 2016 Edition.
Should I even consider looking into the later versions of NFPA 13 (2019-present)? If there are major differences, how do we reconcile following only 2016 since the building code references it even though it may be outdated now? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
15 Comments
Pete H
1/6/2025 06:43:54 am
Yes.
Reply
James E Art Fire Protection Engineer (FPE)
1/8/2025 12:52:59 pm
Worse Buildings.
Reply
Dan Wilder
1/6/2025 07:37:11 am
I would always work to understand what the next edition to be adopted has for changes, additions, and deletions so that there are no surprises from bid time to final. There are cases that later editions help an issue thus providing a better solution and is also expressly allowable as written in Chapter 1 Section 1.5 & 1.7.
Reply
NK
1/6/2025 08:12:45 am
Assuming you're a certified engineering technician working for a contractor, it depends on the project delivery method. If the project is design-bid-build then an A/E team is typically specifying the codes/standards/design criteria you should be using. In this situation you should be estimating and designing to their specifications and an alternative could be proposed, but would be proposed as value engineering for future code compliance, not the minimum required by the AHJ as current adopted/enforced. If the design is delegated (such as a design build project or working directly for an owner) we normally would have a conversation up front in sales about major differences between the minimum requirements and what the newest books say so the client can make an informed decision based on their project budget, schedule, and future goals. The bigger the project the more substantial the cost impact could be so this primarily applies to larger projects (new construction, large retrofits, major existing system modifications, etc) and normally isn't something that would be changed mid-project.
Reply
Glenn Berger
1/6/2025 08:17:02 am
Always be aware of changes and the reasons given for the changes. There have been times where changes are just revisions back to previous editions.
Reply
Todd E Wyatt
1/6/2025 08:28:41 am
Unless the AHJ specifically adopts a different edition of a Referenced Standard (e.g. NFPA 13 – YYYY) per the adopted (scoping) Code (e.g. IBC-2021 or 2024), the Project is ONLY required to meet the minimum requirements of the Referenced Standard edition.
Reply
Adam Jensen
1/6/2025 08:53:26 am
My local code now calls for NFPA 13-2019, but this only came into effect with the new year. Previously, we were on the 2013 edition.
Reply
Jack G
1/6/2025 09:50:30 am
Always stay up to date. Purchase the new code, read and become familiar. Nicet tests usually specify a code edition and it may not be the current edition.
Reply
Jose Figueroa
1/6/2025 11:54:31 am
Both NFPA 13 and NFPA 16 have been updated to the 2025 edition. The term "your area" is somewhat ambiguous—are you referring to your department, customer service, or the design engineering team at a project company? Regardless of your situation, I strongly recommend transitioning to the 2025 edition in all cases. If you're interested in understanding the changes, I suggest conducting a Gap Analysis. I just completed one for Mexico. The client hotel was frustrated with old NFPA 101 references.
Reply
DANEFRE
1/6/2025 03:45:00 pm
I believe they are refering to their state's adopted building code. The building code (or fire code in some states) will dictate the NFPA 13 edition.
Reply
Todd E Wyatt
1/6/2025 01:57:27 pm
Being aware of Code and Referenced Standard revisions from one edition to the next is recommended. Designing to the most recent edition of a Code and/or Referenced Standard that has NOT been adopted by the local jurisdiction is NOT recommended, however, without written permission from the AHJ. Sometimes subsequent editions of a Code and/or Referenced Standard become LESS stringent and designing to these requirements may make your Project noncompliant.
Reply
Jose Figueroa
1/6/2025 03:51:26 pm
Definitely, yes
Reply
Joe Chadwick
1/6/2025 08:17:15 pm
The Code is the collection of lawfully adopted model codes with any modifications listed in the adopting legislation. If a new model code edition isn’t adopted by a governing legislative body, it’s not your Code yet.
Reply
James E Art Fire Protection Engineer (FPE)
1/8/2025 12:43:51 pm
Often codes change for a reason.
Reply