Tire Storage without Sprinklers Whenever the storage of tires is brought up, I often see people focusing on the area, volume, and storage height requirements that necessitate sprinklers.
Looking through IFC requirements to fully understand these triggering design factors, I found the Section “3206.10.1.2 Nonsprinklered Buildings: Aisles in nonsprinklered buildings shall be not less than 96 inches (2438 mm) wide.” Am I correct in understanding that this would require all aisles in between tire racks, as well as a clear walkway around tire rack to be at least 8’ wide? This is something I have never seen in an unsprinklered tire storage setting and would effectively require sprinklers for any efficient for of rack tire storage. Am I understanding this section correctly or am I missing something? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Pete H
9/17/2024 08:08:20 am
If you have tire storage in a nonsprinklered building, you are correct in reading the requirement.
Reply
Joe
9/17/2024 08:38:34 am
Rember that for tires, high pile is at 6ft.
Reply
Dan Wilder
9/17/2024 08:42:34 am
It's not designed to be efficient; it's designed to allow Mechanic Joe & Suzy Public time to exit the area and keep Fire Marshall Bill's responding crews safer.
Reply
Jesse
9/17/2024 11:18:07 am
Pretty much what Dan said. My personal opinion, nothing good comes from unprotected tire storage
Reply