How does the main drain test differ from the hydrant flow test in analyzing a water supply?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Anthony
10/17/2025 07:40:04 am
Several items come to mind: Flow test tells you how much water is at the street/at that hydrant. Main drain test will tell you how much water is flowing out of the base of riser with the limitation of the size of your drain. Main drain is also a check that the city supply and required base of riser pressures are still present within 10% of design conditions.
Reply
10/17/2025 08:06:53 am
They both do it however one big restriction is the amount of water flowing at the visualized residual. That point is critical as it defines the known (0GPM at static pressure to Flowing GPM at residual pressure) from the theoretical (and graph line to the right of the residual flow and pressure).
Reply
Glenn Berger
10/17/2025 08:17:46 am
Validation of the water supply conditions into the building is achieved with the main drain test.
Reply
Jose Figueroa
10/17/2025 11:30:16 am
I remember my early days in Europe, where fire hydrants were seldom private. Conducting a water test on a public hydrant was nearly impossible. The only option available was to attach a pitot gauge to the 2-inch drain test and estimate the available water supply for the sprinkler system.. 😄😄😄
Reply
Mark Harris
10/17/2025 01:37:17 pm
A reasonably current hydrant flow test should be used for system design. The main drain test when comparing from prior years can be helpful for seeing if water supply is deteriorating. Main drain test also confirms valves are open after work was performed. Had a situation once where the street valve was left hand close and the city said it was open. But found out very quick it was not with the main drain test.
Reply
Jack G
10/17/2025 03:04:11 pm
Differences :
Reply
Randy Kimbro
10/20/2025 07:06:44 am
One important item missing in this conversation is the required annual forward flow test. As an AHJ, we still run into many fire protection technicians who think this is a 5-year test. It is not! The annual test requires a flow at the minimum flow rate of the system demand (including hose allowance),
Reply
James Art, FPE
10/22/2025 01:27:38 pm
A very important part is to REVIEW and evaluate the results.
Reply