Design Area for Very Small Extra Hazard Rooms?

3/5/2026

10 Comments

 
Working on the fire protection for a new industrial building. I only have two small areas to protect with sprinklers:
1. 400 ft² hydraulic room
2. 520 ft² transformer room

Both are considered Extra Hazard due to the presence of flammable liquids.

My understanding of NFPA 13 forces me to use 2500 ft² and 0.50 gpm/ft² as the minimum water supply. This will give me 1250 gpm of water to apply to very small rooms, which doesn't make much sense to me.

Am I understanding this right?

Is there a way around it, or a different way of calculating the water supply need?

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Pete H
3/5/2026 06:18:56 am

From NFPA 13 (2025 edition)

As per 19.2.3.1.5, we're only required to go up to 3000 square feet if there are combustible concealed spaces.

As per table 19.2.3.1.1 - Extra Hazard Group 1 under the density/area method directs you to use 0.3 over 2500 square feet and Extra Hazard Group 2 directs to use 0.4 over 2500 square feet.

-

It is entirely possible/plausible that you are getting that 0.5 number from some flammable liquids code in the NFPAs or a separate part of NFPA 13, but my initial thought is that it could possibly be 0.4 gpm over 2500 sq ft.

Though the room design method may also be a goal for you, especially if you additionally calculate the other areas of the building to justify a design with smaller pipe for the areas with lesser hazards.

Reply
Quentin F
3/6/2026 01:27:53 am

Our insurance asked for a 0.5gpm/ft2 density.
Indeed, I think the proper number is 0.4
But that still gives me 1000gpm which seems very high

Reply
Dan Wilder
3/5/2026 07:12:42 am

Ya, there's a bit more to this for information needed.

On the surface, the two rooms, if smaller than the minimum remote area required, would need to be designed with either Room Design (rating of walls and doors for the hazard - likely 2 hour but would need more info) or the "Phantom Flow" requirements of 28.2.4.2.5 (13-25 Edition) would need to be applied due to the actual discharge vs minimum required. Or a possible 3rd case is a FPDBD that details out protection methods.

NFPA 850, 70, 13 and possibly others would also come into the design process review and if this is a water supply path, don't forget hose stream (likely 500 but again, need to confirm).

Reply
Glenn Berger
3/5/2026 08:09:54 am

You have some very good answers so far.

In a new industrial facility - Why is only 2 rooms being considered for sprinkler protection?

Need to review the code analysis and all applicable documents to determine the full extent of where fire protection systems needs to be installed.

Reply
Chad
3/5/2026 09:21:17 am

Glenn is on to something here, kinda odd.

Reply
Quentin F
3/6/2026 01:34:18 am

The rest of the site is protected mostly with fire hydrants.
Some electrical rooms will have inert gaz.

The main activity on site will involve liquid metal which does not mix well with water at all!
Thus the reason why we have limited amount of automated water based fire protection.

Reply
Anthony
3/5/2026 09:38:18 am

I agree with others that the rooms could be designed independent of other areas. Phantom flow can be descoped with an e-mail to the AHJ often.

I'm also concerned with the total project scope of work for a limited sprinkler system, not whole building system for a new build? Odd, makes the architectural compliance more complicated by reducing egress paths and increases wall ratings among other items.

Reply
Dustin T
3/5/2026 09:54:47 am

I too question why you have only two rooms in a new industrial building.

Your information suggests your situation is equivalent to an example in NFPA 13, small high hazard room separated from the surrounding hazard by full height partitions capable of delaying heat from one side fusing sprinklers on the other side. See the guidance in NFPA 13 A.11.1.2 (2016). If this is the case, the surrounding area hazard occupancy dictates the design area size. If the surrounding area is a lower hazard, your demand may be lower than the "phantom flow" option.

Ensure your design's hazard occupancies are correct. In my state, hazard classification and criteria are the role of a licensed engineer.

Reply
RayJ link
3/5/2026 10:27:09 am

Why would you use 2500 ft² when you are only protecting 420 ft² in one area and 520 ft² in the other?

Reply
Jack G
3/5/2026 04:21:33 pm

The way it’s stated in NFPA 13 , phantom flow is only for density area method calculations say an ordinary hazard calculation with a small room that may be extra hazard.
If “ Room design method” is used for the extra hazard room, and the walls and doors/windows of the room were rated appropriately, then the high density applies only to the room with “ no phantom flow “ added.
Density Area vs Room design methods.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT