What is the industry standard or method used for determining the design area size in order to do the hydraulic calculations for Window Sprinklers in terms of the "Adjacent Sprinklers?"
What is the definition of "Adjacent Sprinklers?" Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Dan Wilder
3/14/2025 08:08:36 am
In this case, I take adjacent to be the pendent sprinklers closest to the sprinkler protected glazing (this would include Window Sprinklers but may also include other means). Unless Room Design is being utilized, sprinklers on both sides of the glass could potentially be used.
Reply
Murray
3/19/2025 12:40:19 pm
For the adjacent sprinklers, is it qualified as:
Reply
Glenn Berger
3/14/2025 08:25:38 am
Adjacent sprinklers are those that are near the area of specialty protection, which one has to assume will be concurrently activated.
Reply
Jack G
3/14/2025 10:06:26 am
Directly next to the window.
Reply
Jack G
3/14/2025 10:19:02 am
I didn’t mention but the sprinklers were on the inside of the gallery. Not exterior.
Reply
Murray A
3/14/2025 06:00:30 pm
For the adjacent sprinklers, is it qualified as:
Reply
James E Art Fire Protection Engineer (FPE)
3/19/2025 12:09:20 pm
Used to be San Francisco would accept extra fire sprinklers on the inside of a window that was too close to the property line
Reply