Does maximum pressure and allowed hazard classification for any sprinkler (such as light hazard, 175 psi) really matter in a deluge system?
I have a design situation where I need to use 8.0K extended coverage sidewalls listed for light hazard use, to achieve an FM Global Hazard Category 2 (HC-2), 0.60 gpm / 1,200 sqft, and I cannot accomplish that without exceeding 175 psi. Since the heads are open, I would think that pressure and rating do not matter since the activation will be by electronic devices. Does it matter? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Pete H
7/24/2025 06:21:36 am
Did you use high pressure fittings? And valves listed for higher pressures as well?
Reply
Brett
7/24/2025 06:52:43 am
Yes, they both matter and you'd be opening yourself up to liability if a component failed or the system didn't operate as intended. As far as the hazard classification goes you might need to work with an FM representative if you can't find a sidewall that's approved for HC-2 occupancies. If their datasheet specifically calls out an extended coverage sidewall for an HC-2 occupancy then the sprinkler must exist.
Reply
Glenn Berger
7/24/2025 08:21:35 am
Maximum pressure always matters. There are fittings, valves, and other components that still need to operate correctly.
Reply
Dan Wilder
7/24/2025 08:28:21 am
NFPA 13-19' 7.1.2 Rated Pressure - Components shall be rated for the maximum system working pressure...
Reply
Louie Lincoln
7/24/2025 08:30:29 am
It may matter even more on a deluge system as when it trips the surge is astounding.
Reply
Chris
7/24/2025 08:35:39 am
Not to de-rail the question, but code literally tells us to exceed the rated pressure of fittings for hydro-static tests. Most hydro's end up having a pressure of easily 220psi, and usually the field will pump it up a day before so that it is ready and settled by the time the actual inspection takes place. If this occurs on a Friday, I have heard that systems will go the weekend over 220psi with threaded fittings rated for 175psi and have no issues.
Reply
Anthony
7/24/2025 08:38:02 am
I'm not sure you should use sprinklers listed for light hazard in an HC-2 category design. FM might reject the design. FM has specific sprinklers/nozzles listings for exposure protection that might be worth a look.
Reply
Franck
7/24/2025 10:00:50 am
There is one big concern with high pressure: the water distribution pattern and the water droplet size.
Reply
David Kendrick
7/24/2025 10:18:23 am
Have you checked the possibility of using smaller orifice heads closer to the mains and riser?
Reply
Jack G
7/24/2025 11:17:19 am
Yes it does matter.
Reply
Kenneth Casey Milhorn
7/25/2025 09:28:51 am
Yes, as Franck said, it's not only about the activation element to "hold back pressure", but it's about the spray pattern. The spray patterns and droplet sizes can change dramatically at higher pressures. Also, many of these sprinklers are listed for 250 psi with the exact same "parts", manufacturing process, etc. it's just the fact that the manufacturers didn't spend the money to have them listed at the higher pressures because it wasn't a good ROI. Most likely, the rest of your components are listed to 250 psi or greater. Many times it does come down to the sprinkler head as the limiting factor for system pressure. Worth a call to the manufacturer to see if they will write a letter, especially if they have some documentation of testing they have performed on this head at higher pressures. You never know unless you ask.
Reply
Phil Watkins
7/25/2025 10:26:22 am
I'd be very surprised if you are going to see 175 psi residual pressure at any of your open sprinklers when the whole system is operating (although not impossible of course depending on total system flow rate and water supply performance).
Reply