Can you have two fire sprinkler systems in one area?
A place is looking to charge a fleet of electric vans in an enclosed parking structure. The building already has a wet system designed for Ordinary Hazard Group 2. They want to put in a 16-zone extra-hazard (group 2) deluge system to work alongside the existing wet system. Has anyone heard of this before? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments
Dan Wilder
8/14/2024 08:04:21 am
Can you....with the right detection and releasing equipment yes however, a couple issues come up
Reply
BK
8/14/2024 08:56:14 am
This comment about the separation / baffles cannot be understated. This is paramount to have a chance at an appropriate water supply duration and response.. in addition to all the other comments found here. My approach to this design would still be similar to industrial deluge where adjacent zones may be required simultaneously and requires a large water supply. This should take into consideration fire/heat spread between zones. If more than 2 Adjacent zones cannot be separated by rated partitions, this could be a deal breaker if looking at 16 sizeable zones.
Reply
Anthony
8/14/2024 08:07:52 am
The OH 2 could act as a wet pilot line for the deluge system with proper valving and signaling. I wouldn't but it think it could.
Reply
Jesse
8/14/2024 08:12:55 am
My first gut reaction was "What could go wrong..."
Reply
Glenn Berger
8/14/2024 08:17:33 am
I think that I am missing something here. You want to provide a general area deluge system in the same location as a general area wet-pipe system? Dan's response above raises concerns that I have regarding your question.
Reply
James Phifer
8/14/2024 08:39:16 am
Maybe I'm not understanding this correctly but, this doesn't seem like it would work well. If the Deluge system activates first, that would keep the fusible links on the wet system from activating. If the wet system activates first, that might keep the detection from activating, unless the flow switch triggers activation of the deluge. You would still need to calculate both flows simultaneously.
Reply
Franck
8/14/2024 08:56:11 am
It is quite a common practice in turbine building where you have an area protection by sprinklers below the turbine deck, and some spot deluge protection systems for some key oil-containing equipment (feedwater pumps, seal oil skids…).
Reply
Ricardo Gonzales Jr
8/14/2024 09:05:20 am
I have done this in-flight simulator rooms. The OH2 wet sprinklers were mounted in the ceiling and the deluge were placed 3' from the floor. The units are all hydraulic and the deluge was manual only. The intent was for protecting the cockpits with the sprinklers and if hydraulics were involved in the fire, the deluge to dilute and drain to a separated catch basin where AFFF (3F) is available to extinguish a fire should it travel.
Reply
Joe
8/14/2024 10:08:31 am
Are there any developments/news on an updated design density to reflect today's vehicles coming to NFPA 13 standard anytime soon? OHII hasn't changed since the 1970's when it was a mostly steel car with little plastic and a steel gas tank. Without adding the EV component, today's car is the opposite that testing data is based upon.
Reply
James E. Art, FPE
8/14/2024 03:13:29 pm
Reply
Joe
8/15/2024 11:16:12 am
Thanks Jim, the triple car stackers are a major issue also with lack of tested/proven design density. Combine the triple car stackers and multiple EV chargers in the same enclosed parking garage and residential apartments above is all we seem to be building in New Jersey in our transit villages. It's going to be one heck of a reactive test to the "engineered solution" WHEN the first fire emergency happens.
anon
8/16/2024 09:05:25 am
I have ran into this as well, solution was to have the area become a room surrounded by full height walls.
Reply
Jack G
8/16/2024 09:28:07 am
Good choice. I wholly agree.
Reply
Jack G
8/16/2024 09:17:58 am
My main concern would be would both design densities. Deluge usually means “ all in “ open heads like exposure systems. Will the OH 2 system above be activated, I think so, and when the 2 systems are calculated simultaneously, the higher flow and pressure would make the Oh 2 heads flow at a much higher flow and pressure, with the oh2 pipe sizes. ( may read not sufficient )
Reply