I have a non-combustible shell building with 18-inch steel beams under corrugated metal deck.
Some of the beams are spaced in excess of 7'-6" apart, but not exceeding 9'-6" and creating an area exceeding 300 sq. ft. To loosely summarize definitions, per NFPA 13, 2019 edition Section A.3.3.41.1 for Obstructed Construction, Beam and Girder Construction, the steel beams are to be spaced between 3 ft. up to 7½ ft. Panel Construction requires that all cross-sectional areas be filled including the interface at the roof, (which this is not the case on my project), and not exceed the 300 sq. ft. area. My question is this, since this building does not meet either criteria and is not combustible construction, (no wood is being utilized in the structure), there are no concrete tees being utilized and there are no bar joists present, would this then be considered as Unobstructed? My thoughts are no, and that this is still Obstructed Construction, however I can't find a proper definition within the Obstructed Construction definition. I am wanting to know if I can utilize the 1" to 6" below Obstructed Construction allowance however I am held up by the definition of the construction type and am unsure if I need to space within the bays or if I can space below the 18-inch steel beams. Any thoughts or input on this would be greatly appreciated. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
16 Comments
Anthony
4/24/2023 07:08:03 am
If its not obstructed construction then it's not, there is no grey area.
Reply
Glenn Berger
4/24/2023 08:05:34 am
For obstructed construction construction, the requirement is 7'6" or less with deep beams.
Reply
Larry Appel
4/24/2023 08:26:52 am
Glenn is correct, you’re describing an unobstructed application!
Reply
Dan Wilder
4/24/2023 08:31:14 am
How deep is the pan deck?
Reply
Jeffrey Davis
4/24/2023 10:28:19 am
The deck is made up utilizing Robinson decking.
Reply
Dan Wilder
4/24/2023 04:54:11 pm
Any pan decking greater than 3" deep you need to measure to that high point which can greatly affect the deflector distance clearances.
Todd E Wyatt
4/24/2023 08:47:18 am
2019 NFPA 13 references “obstructed” or “obstruction” (277) times.
Reply
Todd E Wyatt
4/24/2023 08:47:39 am
REFERENCES
Reply
danefre
4/24/2023 09:21:33 am
That ceiling pocket part is important. You cannot apply the ceiling pocket section for bays created by structural members. Ceiling pockets are architectural features!
SCHULMAN
4/24/2023 08:49:24 am
Unobstructed for the win ... but I am curious so I want to expand the discussion if that is fair ... what if the ultimate goal is to have lay-in (ACT) ceilings throughout. (creating a non-combustible ceiling space). He did say "shell" space afterall ... do you place upright sprigs and have the tenant contractor run the flexheads? Would you then disregard beam spacing with exception of sprigs that end up too close to beams ... so you'd add one or two along a run to re-space for that? ... For a code compliant shell space that won't be used as installed ... ? Any contractors out there who care to weigh in ?
Reply
danefre
4/24/2023 08:56:16 am
We usually do both shell and tenant work for our contracts. We put the sprigs on 1" tees with a plug on the bull. That outlet will later be used for the flexhead.
Reply
SCHULMAN
4/24/2023 09:53:06 am
Thank you sir.
danefre
4/24/2023 08:50:33 am
You can have beams spaced more than 7'-6 and still have obstructed construction as you indicated. Some of the above responses are misleading.
Reply
Jesse
4/24/2023 09:25:58 am
As you have described it, I see this as unobstructed construction.
Reply
Jeffrey Davis
4/24/2023 10:37:37 am
Thank you guys for your help clarifying this for me. It has helped give me more to think about in regards to obstructed and unobstructed construction.
Reply
4/16/2025 08:29:49 am
In a non-combustible building with 18-inch steel beams spaced between 7'-6" and 9'-6" apart, creating areas exceeding 300 sq. ft., the construction does not fit neatly into NFPA 13's definitions of obstructed or unobstructed construction. While some professionals suggest it may be considered unobstructed, others recommend consulting with the Authority Having Jurisdiction (AHJ) for a definitive classification and guidance on sprinkler placement.
Reply