Could anyone point me to statistics to show how likely a single interlock pre-action sprinkler system is to spuriously or falsely activate?
A client is concerned about possible water damage in a high-voltage switchroom that could damage their gear and cause a lengthy business interruption. I have tried examining NFIRS data, but its format makes it difficult to analyze without a background in relational databases. I would like to explain the relative risk to the client in terms of 'it's a 1 in 100,000-year event you are concerned about' or whatever the stats point to. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Ricardo Gonzales
11/18/2025 08:39:58 am
This would be a situation where I would have a sit down with the AHJ to eliminate the sprinkler system and put in a clean agent system. Contact NFPA and ask about their Electrical Danger data base. That may help.
Reply
Josh
11/18/2025 09:22:30 am
I'm with you on this one. You'd have to convince ME to put any type of water delivery system in a room like that.
Reply
matt
11/19/2025 02:31:06 pm
Thanks, appreciate the comments. My workscope is actually to do a risk analysis and evaluate for the client choosing between a pre-action system, gas flood or nothing in their HV room. (rest of the building will be sprinkler protected). Without running numbers, leaning already towards gas flood :) Will look into arc flash detection/protection...
Reply
Mark
11/18/2025 09:23:08 am
NFPA 2001 Clean Agents states over 480 volt design should be based on fire test. Manufacturers have not done any full scale tests. FM Global does have criteria in loss prevention sheet 4-9.
Reply
Chad
11/18/2025 09:36:29 am
"High Voltage"---- is this transmission and distribution or just 480?
Reply
Franck
11/18/2025 09:45:24 am
Stats for wet system spurious activation is 1 to 13 000 000 in terms of installed sprinklers
Reply
Nick
11/24/2025 11:25:02 pm
The stat for spurious activation is often trotted out, but it's not actually that useful. It's actually the number of heads that fail "spuriously" due to a manufacturing defect or incorrect install. The stat does not include the actual top contenders of activations when there is no fire. If you look through the NFIRS data the other top reasons are a heat source (oven etc), freeze damage, mechanical impact, corrosion, and deliberate tampering (jails/schools/hospitals etc.)
Reply