Coverage of Window Sprinkler for a Tall Facade?

4/24/2025

4 Comments

 
I am trying to understand the criteria for designing window sprinklers for a tall glass space.

The application is a very large façade greater than 300 feet (91 m) long and 45 feet (14 m) high. The vertical mullions are 14'-9" center to center (4.5 m).

What is the definition of a story, and how does it apply as stated in NFPA 13 8.7.8.1 "A single line of sprinklers is permitted to protect a maximum of two stories of wall area or two levels of vertically aligned windows where architectural features are sufficiently flush to allow rundown?"

This height seems like it would be well above a two-story height, but what would that be reasonably defined as?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Pete H
4/24/2025 09:44:26 am

In NY Fire Code "Story" is defined as:

That portion of a building included between the upper surface of a floor and the upper surface of the floor or roof next above (see "basement", "building height", "grade plane", and "mezzanine"). A story is measured as the vertical distance from top to top of two successive tiers of beams or finished floor surfaces and, for the topmost story, from the top of the floor finish to the top of the ceiling joists or, where there is not a ceiling, to the top of the roof rafters.

----

In my opinion, "story" doesn't really apply to your situation due to the lack of floors.

However, "two levels of vertically aligned windows" may very well apply, as I doubt the facade is one singular 45 foot tall by 300 foot wide piece of glass. So how tall are the windows?

If this does not work, another tactic might be to take the story distance where the building actually does have two floors and apply the worst case scenario.

Either way, I'd say please make sure there's some form of baffle keeping your lower "level" of sprinklers from being cold soldered by the ceiling level.

Reply
Dan Wilder
4/24/2025 09:50:07 am

So there is a slight description issue I wanted to ask about....

You are asking about providing sprinklers for exposure protection as allowed within 8.7 (2019 Edition of NFPA 13, possibly later editions but this is the one open in front of me currently).

The definition of 'Story" in the IBC is "...portion of the building included between the upper surface of a floor and the upper surface of the floor or roof next above..." (in a nutshell)

Window sprinklers (Like the Tyco-WS & the Reliable WP) has specific installation criteria for widow width, height, and other factors so watch for those. I don't think the height will be the limiting factor so much as trying to get the correct GPM for the window that large without multiple levels.

I have seen a story be al little as 9' and as large as 50' so not sure there is a height limiting factor for that definition.

Reply
Todd Delisle
8/22/2025 11:09:14 am

Most window sprinklers that I have found to date limit the MAXIMUM EXPOSED HEIGHT OF GLAZING to 13'-0", I'm looking for a head right now that allows more.

Reply
Jack G
4/24/2025 12:23:00 pm

While the applicable use of fire sprinklers for the protection of windows appears to be a simple process it is, in accuality a rather complex consideration.
The first is to understand what a window sprinkler is and is not, and how to appropriately integrate them into the sprinkler design of the building; this is a much more complicated process than one might assume. Nfpa 13 treats window sprinklers as " special application sprinklers", and does not include design parameters in its text. Section 8.15.26 was added in the 2016 edition and gives limitatiins on when they max be installed,/ used.
For this reason, window sprinklers should be incorporated into the design by the A&E design
Proffessional and it is they that should present the design to the AHJ.
Section 104.1 of the IBC refers to aternate material, methods of construction and equipment. and gives latitude to utilize the use of window sprinklers in lieu of fire rated glass.
Time of separstion ( up to 2 hrs)
Look to see if the walls are fire walls( non load bearing fire walls as in IBC 707.
WS are not allowed in areas where frequent .
Detonation occur.
The building must be protected with 100% sprinkler protection.
Size of glass. must be vertical not sloped or curved
Glass must be at least 1/4 inch thick and tempered.
and must be fixed glass.
The IBC 404.6 allows for closely spaced sprinklers to be utilized with rated glass and frames as an alternate to the 1 hour separation for atriums. This allowance gives a sprinkler designer the luxury of using sprinklers that are specifically listed for glass per nfpa 13 11.3.3 for water curtains.
For 2 hour separations window sprinklers are used on the interior and exterior glass and must be installed per the listed manufacturers design/ data sheet.
For closed space sprinklers are used 15 gpm per liners foot dhould be used or 20gpm for sprinklers 6-8 ft on center. The length of the hydraulic length of the remote area determines the quantity.
The ooenings in the wall and the depth of the horizontal mullies will determine how many levels to be used.
Consult your manufacturerds databsheet for the approved installation.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '25 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    Nfpa-409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE 100-Day Marathon
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT